Hello, Im trying to do a substation model with Etap computer program, here I have got a 2,4/6,9/13,8 Kv , 16 000 Kva , Z= 7% autotransformer, Etap requires the impedance(+) between PS,PT,ST.
this is the help info grom ETAP:
"Positive and Zero Sequence Impedances
For 3-winding transformers, specify three impedance values in percent on the primary winding MVA base:
Zps = Leakage Z between the Primary and Secondary windings with the Tertiary winding open circuited.
= Rps + j Xps = Rp + Rs + j ( Xp + Xs ) % (base MVA = MVAp)
Zpt = Leakage Z between the Primary and Tertiary windings with the Secondary winding open circuited.
= Rpt + j Xpt = Rp + Rt + j ( Xp + Xt ) % (base MVA = MVAp)
Zst = Leakage Z between the Secondary and Tertiary windings with the Primary winding open circuited.
= Rst + j Xst = Rs + Rt + j ( Xs + Xt ) % (base MVA = MVAp)
These are the nameplate impedances of the transformer; no further calculations are needed to extract the impedances of the 3-winding representation, as ETAP already does this internally "
---------------------------------------------------------------------------------------------------------------------------------------------------------------------
The problem is that my autotransformer Namplate only show this parameter Z=7%, does that mean that Zps=Zpt=Zst= 7% ? Anybody knows how could I get Zps,Zpt,Zst.
I really Appreciate your Help.
Thanks.
Adrián.