Selecting the Appropriate Core Cable for Powering a Motor

01/26/2010 2:41 AM

Dear Team,

We are using squirrel cage induction motors operating on 410 V, 3 phase, 50 Hertz power supply. The same are used to drive pumpsets for fire fighting.

The larger kW pumpsets are started with star-delta starters and the smaller kW pumpsets are started with Direct-on-line starters.

My doubt is some consultants use 3 1/2 core cable to power the motors - The fourth core is for neutral which has area of cross-section which is roughly half of the other three cores. Some consultants specify 3 cores.

Please clarify which is most appropriate? We do not normally provide bearing temperature detectors, etc. like in huge Industrial Motors.

Any website showing the particulars will be very useful.

Thanking you,

K. Muthukrishnan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#1

Re: Selecting the Appropriate Core Cable for Powering a Motor

01/26/2010 8:08 AM

For all practical purposes, a 3 core cable is sufficient to power the motor irrespective of the fact that the motor winding is in star or delta.

If a 3.5 core cable is used, then the fourth core is used for earthing of motor terminal box. It is not used as "neutral" while delivering power to the motor.

For a star connected motor, the neutral point will be located inside the motor. It may also be brought out (3.3kV and upwards) for the purpose of starting/protection. But, the fourth core is never used as neutral.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: Selecting the Appropriate Core Cable for Powering a Motor

01/26/2010 10:53 PM

The 3 and 3 1/2 core for a motor does not matter in squirrel cage motor, UNLESS it is continuously running in star mode. Independent of any other sensor devices, 3 phase supply via 3 core will operate the motor. anand sk feedback@maintenancecircle.com

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#3

Re: Selecting the Appropriate Core Cable for Powering a Motor

01/27/2010 1:55 AM

Dear Mr. Muthukrishnan,

Since your application of motors is for fire fighting, the normal method of selection of motors,cables and switchgear is not applicable for fire fighting pumps.

The electrical parameters are taken 2 or 3 steps higher for fire fighting. this is due to the reason that even is the motors, cable or switchgear gets damaged, its not important. the life and building property gets more priority. the cost of replacing life(which is invaluable) and building is much more than the electrical equipment for fire fighting. for more clarifications, mail me at shanbhag@sequentindia.com

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Selecting the Appropriate Core Cable for Powering a Motor

01/27/2010 3:19 AM

If the motor is to be switched from star to delta remote from the motor, then a 7-core cable is required between the starter and the motor: 2 cores for each phase and 1 for the earth conductor.

If the starter is mounted on the motor and a connection made simply to the starter then a minimum 4-core cable is required and possibly a 5, depending on whether a neutral is required. A 4-core carries the three phases and earth. A 5-core carries the three phases, a neutral and an earth.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Electronaut (1); PWSlack (1); shanbhag (1)

Previous in Forum: Lead Acid Battery   Next in Forum: Isochronous Communication
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement