CT Selection for Differential Protection

01/28/2010 4:06 AM

I have a transformer rated 11000/440V,50 Hz,1500kVA. the primary current is 100A and secondary current is 2000A. If is want to use differential protection, then i need to consider class PX CT on both primary and secondary sides. the problem is. the primary voltage is 11000V and secondary voltage is 440V. how do i select class PX CT considering the different voltage levels. Will the CT give output in case there is internal fault in the CT.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Selection of CT for Differential Protection

01/28/2010 1:53 PM

The CT works by measuring and converting the current (based on the CT primary/secondary winding ratio), it doesn't measure the voltage like a standard transformer.

http://en.wikipedia.org/wiki/Current_transformer

You just need to choose current transformers (CT) that are insulated for the voltages in question. It is no big deal, these CTs are standard and can be brought off the shelf or cheaply made to order.

Check your differential relay (or whatever devices you are using for differential protection) for what CT secondary current and burden you need (should be either 5A or 1A with a burden of say 5VA).

Talk to a CT supplier or manufacturer for more details and advice (or check out their websites).

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#2

Re: CT Selection for Differential Protection

01/31/2010 5:55 PM

CTs are availble for diffrent voltage levels, the problem is where your concerntration lies. CTs on primary and secondry will indicate according to their current ratio, the most important thing to concider is that their out puts will reflect their respective inputs and will not exceed the normal CT out put range of 5 or 1 Amp. If the insullation class of ur CTs is achieved for the respective voltages and the CTs are of same burden, ur free to do any thing u want to do with it.

Dickson.

__________________
There is peace in silence and achievement in plans.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: CT Selection for Differential Protection

04/10/2010 7:46 AM

As per my knowledge, differential CTs are not required for transformers of rating 1.5 MVA. They are used for transformers above 5 MVA (= 5000KVA).

Please cross check your specifications.

Regards,

Prashanth Gaitonde

Hyderabad

Register to Reply