Buffer Tank Sizing

02/01/2010 7:47 AM

Hi, I want to install a buffer chilled water tank for our process chiller,

Process Chiller Capacity : 230 ton.

System Chilled Water : 10 m3

is it possible or not.

If yes, what are the proper equitions to calculate the buffer tank size ?

Thank You

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Buffer Tank Sizing

02/02/2010 7:02 AM

Calculate the total heat load of the system

Q = m cp (Tr - Ts)

then,

V = Q / (ρ * cp * Δ T)

take care the units.

Reply
Associate

Join Date: Jan 2010
Location: Charleston, SC
Posts: 25
Good Answers: 1
#2

Re: Buffer Tank Sizing

02/03/2010 7:45 AM

You are smart to think about this. A lot of people overlook buffer tanks. The buffer tank is used if the chiller system volume is too small. A small system volume will cause short cycling of the chiller. Each chiller has different requirements for minimum system volume. Start by calculating your system volume including chiller and all piping. Then consult the chiller rep.

__________________
R. Turner, P.E.
Reply
Anonymous Poster
#3
In reply to #2

Re: Buffer Tank Sizing

02/03/2010 11:34 PM