What power rating is it? What else is on the plate?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
You will need to know a little more about your, but here is a reference for all standard winding patterns used by motor mfrs. The 208-230V issue has only to do with the range. What they do is design it for 220V +- 10%, so that covers 200-240V systems. You will only have 2 connection patterns to deal with, but you will need to know if it is Y or Delta wound. The motor nameplate should tell you.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Here's a sample data tag. As was said, you need to know if your motor is wye or delta wound. If the tag on your motor looks like this you're in business. If not, let us know. Also low voltage is either the 208 or 230 and high is the 460. Be advised these are NEMA configurations. There may be differences if you're an IEC kind of guy.
__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
The motor is configured so that you can use either voltage. High or low. Strap the motor for the existing power at your facility. No need to go to the extra expense of obtaining a xfmr. I'm thinking you might want an electrician to check your work before you flip the switch.
__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein