Dual Voltage Motor

02/01/2010 10:16 AM

Can any one please clarify me how to make a power as well as control wiring for a dual voltage motor?

recently i came across a motor whose voltage detail in name plate was 208-230/460 V

and it was a 9lead dual voltage WYE Connection.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Dual Voltage motor

02/01/2010 11:22 AM

What power rating is it? What else is on the plate?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Dual Voltage Motor

02/01/2010 11:50 AM

You will need to know a little more about your, but here is a reference for all standard winding patterns used by motor mfrs. The 208-230V issue has only to do with the range. What they do is design it for 220V +- 10%, so that covers 200-240V systems. You will only have 2 connection patterns to deal with, but you will need to know if it is Y or Delta wound. The motor nameplate should tell you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
2
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: Dual Voltage Motor

02/01/2010 3:13 PM

Here's a sample data tag. As was said, you need to know if your motor is wye or delta wound. If the tag on your motor looks like this you're in business. If not, let us know. Also low voltage is either the 208 or 230 and high is the 460. Be advised these are NEMA configurations. There may be differences if you're an IEC kind of guy.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Feb 2008
Posts: 18
#4
In reply to #3

Re: Dual Voltage Motor

02/01/2010 9:37 PM

Dear RDGRNR,

your comment is exactly right, but the thing is in low voltage terminals should i provide a 3 phase 208 - 230 V supply through transformer.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#5
In reply to #4

Re: Dual Voltage Motor

02/02/2010 10:17 AM

The motor is configured so that you can use either voltage. High or low. Strap the motor for the existing power at your facility. No need to go to the extra expense of obtaining a xfmr. I'm thinking you might want an electrician to check your work before you flip the switch.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply