How do you determine your size of your capacitor bank? Site some examples. Looking forward for some replies. Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Capacitor Bank

02/03/2010 4:58 PM

Are you looking for the size of a capacitor or do you need a KVAR size for PF correction?

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 18
#2
In reply to #1

Re: Capacitor Bank

02/05/2010 8:04 AM

KVAR size for PF correction. How can i determine the KVAR rating of the capacitor bank?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3
In reply to #2

Re: Capacitor Bank

02/05/2010 6:32 PM

look to the right of the screen and find Search This Forum. Enter "KVAR for power factor correction.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Capacitor Bank

02/06/2010 9:47 AM

kVAR of Capacitor required = kW (Tan phi 1 - Tan phi 2),

where,

kW is the connected load

phi 1 = power factor angle (Cos inverse) of existing power factor

phi 2 = power factor angle (Cos inverse) of target power factor