Dear Gentlemen,
How do you determine your size of your capacitor bank? Site some examples. Looking forward for some replies. Thank you.
Re: Capacitor Bank
02/03/2010 4:58 PM
Are you looking for the size of a capacitor or do you need a KVAR size for PF correction?
Re: Capacitor Bank
02/05/2010 8:04 AM
KVAR size for PF correction. How can i determine the KVAR rating of the capacitor bank?
Re: Capacitor Bank
02/05/2010 6:32 PM
look to the right of the screen and find Search This Forum. Enter "KVAR for power factor correction.
Good Answers: 170
Re: Capacitor Bank
02/06/2010 9:47 AM
kVAR of Capacitor required = kW (Tan phi 1 - Tan phi 2),
where,
kW is the connected load
phi 1 = power factor angle (Cos inverse) of existing power factor
phi 2 = power factor angle (Cos inverse) of target power factor