AS IT HAS VERY HIGH FREQUENCY CAN WE TEST OUTPUT VOLTAGE/ CURRENT OF VFD WITH MULTIMETER ?
Re: VFD
02/04/2010 10:41 AM
Re: VFD
02/04/2010 11:10 AM
Good Answers: 29
Re: VFD
02/04/2010 11:14 AM
Current; use an amp-clamp.
Voltage; A digital multimeter operates on it's own clock. If the VFD output frequency happens to fall on a harmonic of this clock the meter will never settle down, so use an analog if you can. Also, remember, output voltage will be proportional to frequency based on input voltage.
Good Answers: 50
Re: VFD
02/08/2010 6:49 AM
If you use a 1000:1 CT, for example, you mostly get a good reading of current. The voltage is much more difficult, the easy answer is an (older?) analogue multimeter with moving indicator rather than a DMM, otherwise, you need quite a good quality analyser to get an accurate result.
These readings are normally part of the VFD display, good quality VFD, good readings. Why do you want to measure separately?