Fault Level Current

02/04/2010 2:29 PM

Hi guys

On our Plant we have two transformers (22kv/525v;delta/star) supplying the MCC's in the substation, each transformer supply different section/panels and they are equipt with a bus coupler in between in case when one fails we can switch over to another one.

My question is:As far as the fault level current is concern, what will happen if i parrallel this two transformers for few min. (e.g 2min) and what's the danger involved.

I search on previous discussion on CR4 but i didnt get the specific answer.

__________________
Dan Segami
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Fault Level Current

02/04/2010 4:48 PM

Your fault current will be approximately double in value. The danger is if the fault occurs during that 2 minutes you equipment is toast if it is not rated for the max fault condition.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2

Re: Fault Level Current

02/04/2010 10:02 PM

The fault level will be double the current supplied by individual transformers. If your protection system is not adequate and the MCC is not designed for this fault level, it can lead to major breakdown of the system.

It has to be verified whether adequate protections are in line before such an attempt.

Register to Reply
Anonymous Poster
#3

Re: Fault Level Current

02/05/2010 12:40 AM

simple; you can do but it is a calculated risk. During paralleling, fault should not occur. Normally only momentary paralleling is allowed.

rc sachdeva

919967642157

Register to Reply
Anonymous Poster
#4

Re: Fault Level Current

02/05/2010 12:44 AM

Its simple. When you parallel two transformer and if the fault occur, the switchboard will be subjected to double the fault current. The switchboard fault withstand is defined as 1 sec rating basis. It is not advisable. But still we do the momentary paralleling i.e. paralleling through interlock; which is like instantaneous operation. There is a calculated risk in paralleling the two transformers for 2 min. Nothing will happen if there is no fault during parlleling. Operating persons do take this kind of risk when a large rated motor to be started.

rc sachdeva

09967642157

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#5

Re: Fault Level Current

02/05/2010 3:21 AM

Dear Mr. Daniel,

Please check my profile and go through the thread main tie main redundant system. your question is very similar to one posted

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#6

Re: Fault Level Current

02/05/2010 3:23 AM

Dear Mr. Daniel,

please check this thread http://cr4.globalspec.com/thread/48170#newcomments

Main Tie Main, redundant Bus tie breaker

Thanks

Register to Reply
Anonymous Poster
#7

Re: Fault Level Current

02/08/2010 2:18 AM

Dear Friend,

Synch. of two or more transforments needs to check and fulfilling of synch. conditions, without which there will be danger of mixing two souces of different sources roughly.

CVS Murthy

Register to Reply