Generator Sizing

02/04/2010 4:03 PM

how can i find the generator sizing for a villa with 200kw connected load.

note that he should work only on 75% of his full capacity.

thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Generator sizing

02/04/2010 4:44 PM

Your local code should provide a reference for you. If not, check Article 220 of the NEC.

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 20
#3
In reply to #1

Re: Generator sizing

02/05/2010 6:54 AM

I am, not sure your answer was any help for this question. Not too many people have the NEC hand book handy. The question was answered very well from an India by giving the person the required kVA generator. Actually, I the 200 KV was a lot for a villa. A 350 kVA genset will probably have a 6 cyl diesel engine.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2

Re: Generator Sizing

02/04/2010 9:53 PM

Assuming a power factor of 0.8, the kVA rating of the generator will be 200kW/0.8 = 250kVA.

Generator rating = 250kVA/0.75 = 333.33kVA. The nearest standard rating is 350kVA on the higher end.

The rating of the DG set will be 350kVA (280kW at 0.8pf).

This is a rough calculation. You need to follow the norms applicable to your area while selecting an appropriate genset.

Register to Reply
Participant

Join Date: Feb 2010
Posts: 3
#4

Re: Generator Sizing

02/05/2010 1:55 PM

thank you all

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Generator Sizing

02/05/2010 6:17 PM

jwait55

The point I wanted to make was that either the local code or the NEC gave the criteria to calculate the load in the villa and from that the generator size could be determined. If the villa had a connected load of 200 kw, then the OP must determine what the calculated load will be. You don't take 75% of the 200 kw to size the transformer. The actual load demand may be only 75 kw.

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 20
#7
In reply to #5

Re: Generator Sizing

02/05/2010 11:04 PM

I agree, the connected load +/- should be the determining factor for sizing a stand-by genset. I have a 15kVA Kabota generator which runs my computers & airconditoners & lights. I just calculated the total load in amps & converted to kVA to size my generator. I don't think this is a very complicated calculation as lonf as you know the connected load.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Generator Sizing

02/05/2010 7:34 PM

Wareagle quote "the point I wanted to make was that either the local code or the NEC gave the criteria to calculate the load in the villa and from that the generator size could be determined. If the villa had a connected load of 200 kw, then the OP must determine what the calculated load will be. You don't take 75% of the 200 kw to size the transformer. The actual load demand may be only 75 kw."

This should read "you don't take 75% of the 200 kw to size the generator"

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Electronaut (1); jwait55 (2); RONYMAHA (1); wareagle (3)