CHOICE OF ELCB

02/07/2010 1:40 AM

THERE IS A OUTGOING FEEDER (PLANT LIGHTING) RATED 25A CONNECTED THROUGH A MCB OF 25A AND AN RCCB(ELCB). THE ELCB SELECTED WAS OF 40A 100mA. MY QUESTION IS CAN WE USE 25A 30mA RCCB FOR THE SAME LOAD? ....WAITING FOR AN ANSWER....

__________________
shamith gambhir, electrical engineer
Register to Reply
Pathfinder Tags: elcb
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#1

Re: CHOICE OF ELCB

02/07/2010 2:37 AM

PLEASE TURN OFF CAPS LOCK

ANSWER:

Yes, you can use.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2

Re: CHOICE OF ELCB

02/07/2010 3:58 AM

There is nothing wrong in installing a 30mA RCCB in place of 100mA. In fact, a 30mA RCCB is more sensitive than a 100mA RCCB.

A 30mA RCCB is used when you require additional protection against direct contact with live part of the system and also if the earth loop impedance is high (upto 1667 ohm).

A 100mA RCCB is used for protection against indirect contact with live part of the system and for an earth loop impedance upto a maximum of 500ohm.

In your case, 30mA RCCB may cause nuisance tripping of the lighting feeder for small leakage currents.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#3
In reply to #2

Re: CHOICE OF ELCB

02/07/2010 8:33 AM

Thanks dude...so you r suggesting me to use 100mA rccb to avoid nuisance problem i right?

__________________
shamith gambhir, electrical engineer
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#4
In reply to #3

Re: CHOICE OF ELCB

02/07/2010 12:10 PM

Yes. But you have to use a 30mA RCCB if the earth loop resistance is high.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#6
In reply to #4

Re: CHOICE OF ELCB

02/07/2010 11:37 PM

THANKS a lot.....one more question...is it possible to use a rccb for a dc system?

__________________
shamith gambhir, electrical engineer
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#7
In reply to #6

Re: CHOICE OF ELCB

02/07/2010 11:54 PM

Dear all,

Not all Rccb's are not AC/DC type. Some Rccb, such as ABB F200B is for both AC and DC.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#8
In reply to #7

Re: CHOICE OF ELCB

02/08/2010 3:18 AM

but is there any rccb for dc system available in merlin gerin or schneider?

__________________
shamith gambhir, electrical engineer
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#5
In reply to #2

Re: CHOICE OF ELCB

02/07/2010 8:57 PM

Dear all,

I think, 30mA : 1667Ω 100mA : 500Ω is for TT system.

For TN system, the earth loop impedance can be much higher.

For instance, 230V / 30mA * 0.8 = 6100 Ω and 230V / 100mA *0.8 = 1800Ω.

Regards.

__________________
Akihito Shigeno @ JGC-Indonesia