THERE IS A OUTGOING FEEDER (PLANT LIGHTING) RATED 25A CONNECTED THROUGH A MCB OF 25A AND AN RCCB(ELCB). THE ELCB SELECTED WAS OF 40A 100mA. MY QUESTION IS CAN WE USE 25A 30mA RCCB FOR THE SAME LOAD? ....WAITING FOR AN ANSWER....
There is nothing wrong in installing a 30mA RCCB in place of 100mA. In fact, a 30mA RCCB is more sensitive than a 100mA RCCB.
A 30mA RCCB is used when you require additional protection against direct contact with live part of the system and also if the earth loop impedance is high (upto 1667 ohm).
A 100mA RCCB is used for protection against indirect contact with live part of the system and for an earth loop impedance upto a maximum of 500ohm.
In your case, 30mA RCCB may cause nuisance tripping of the lighting feeder for small leakage currents.