Industrial Lighting

02/07/2010 4:58 AM

How to Calculate Inside PLant, Conveyor Gantries, MCC Room & control Room Lighting in 300KW Industrial Plant including no. of Fixtures & Position of Light Points.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Industrial Lighting

02/07/2010 8:59 AM

Assuming you want to purchase industrial lighting for your plant, ask your industrial lighting supplier to figure the requirements.

If you are the industrial lighting supplier, good luck.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Industrial Lighting

02/07/2010 12:53 PM

The inverse square law will be vastly helpful in setting up the calculation for illumination intensity. Depending on my mood at the time, I would use a calculator, spreadsheet or mathematics software to do the calculation. Slide rules are just to tedious.

(Just feeling a little snarky I guess.)

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Nov 2007
Location: Third Rock from the Sun (?)
Posts: 76
Good Answers: 8
#3

Re: Industrial Lighting

02/07/2010 10:35 PM

Good Answer Lyn Lynch. When I saw the question I just absolutely had to check the comments. Back in ancient times when I had a project involving lighting the dealers/suppliers were always more than willing to give me a hand in calculating the needs, thus their sales, for the project.

BTW. I'm in Kabul. Your folks still in the area? You can answer me on the private side as I'll be checking back in later today.

__________________
vagabond
Register to Reply
Participant

Join Date: Nov 2007
Posts: 3
#4

Re: Industrial Lighting

02/07/2010 11:41 PM

Number of fixtures depends upon Average lux level required. Generally lux level adopted is 300 lux for control room, 200 lux for switchgear room, 70 lux for conveyer galleries and100 lux for stair case. Besides, for lighting design following maintenance factors shall be adopted : 0.8 for Airconditioning area, 0.7 for non aircondioning area and 0.6 for dustprone area. These data can be furnished to the lighting fixture manufactures, and they will design and calculate number and type of lighting fixtures .

thanks

Register to Reply
Power-User

Join Date: Apr 2008
Location: Indiana
Posts: 331
Good Answers: 10
#5

Re: Industrial Lighting

02/08/2010 9:20 AM

I agree with lynlynch. An analysis by a lighting engineer is required. Calculating lighting is more complicated than a simple equation. A plant layout has to be set up with the identified lighting requirements for each area of the plant. Then, you can calculate what level of lighting you need where.

One extra note to remember: Ask for 5000 kelvin or higher color temperature lighting. There have been many studies showing increased production.

__________________
"We cannot sow thistles and reap clover. Nature simply does not run things that way. She goes by cause and effect." Napoleon Hill
Register to Reply
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#6

Re: Industrial Lighting

02/08/2010 10:16 AM

I recommend you start reviewing Article 220 in the NEC....That will get you started.

This Article will address Commercial lighting loads then most of your other questions will also be in the (NEC) book. It is a very good minimum standard safey guide. Mark

__________________
Mark Abell
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

lyn (1); MasterEmaybe (1); redfred (1); Tarun Bhatia (1); vagabond (1); WWkayaker (1)

Previous in Forum: CHOICE OF ELCB   Next in Forum: Cheap Timer

Advertisement