Fault MVA

02/08/2010 4:57 AM

what is the fault MVA ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Fault level

02/08/2010 6:05 AM
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Fault level

02/08/2010 9:26 AM

If you know the fault current value and the system voltage, the fault current MVA

= √3 x Fault current in kA x Voltage in kV (for 3 phase system)

= Fault current in kA x Voltage in kV (for single phase system)

- MS