Differential Relays

02/09/2010 1:25 PM

In any ground fault or short circuit fault in our 11kV line the Differential relay of our 132/11 kV transformer always trips our main 132kV circuit breaker before the tripping of local nearest circuit breaker? How can I resolve this problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: differential relay

02/09/2010 1:47 PM

Are you using your differential relay to trip both your 132kV circuit breaker AND local (11kV) circuit breaker (by paralleling the both circuit breaker trips)?

If not (ie- the local and 132kV circuit breakers operate independently of each other), then it sounds like you have not got your protection coordination set correctly. Check the trip curves and operation speed of both your circuit breakers to ensure proper protection coordination.

__________________
jack of all trades
Register to Reply
Anonymous Poster
#2

Re: Differential Relays

02/09/2010 11:36 PM

For any fault out the zone of differential relay range,the diff relay should not trip.

Please give the sld,relay locations and trip circuit details to advise properly.

Register to Reply
Anonymous Poster
#3

Re: Differential Relays

02/10/2010 12:44 AM

ADMIN: Deleted Content

From the Rules: Do not post personal contact information on the forum space. You can share this information via the forum's internal messaging system.

Register to Reply
Anonymous Poster
#4

Re: Differential Relays

02/10/2010 2:46 AM

If you asking this then you are not qualified to be dealing with protection of these devices.....I recomend that you cantact a High Voltage company do assist you.

Register to Reply
Associate

Join Date: Oct 2009
Location: kuruman NC. SOUTH AFRICA
Posts: 51
Good Answers: 1
#5

Re: Differential Relays

02/10/2010 5:17 AM

There is what we call discremination of faults, so definately there is a problem on your setting. dont take chances get the HT company to help you with the sittings.

__________________
Dan Segami
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Differential Relays

02/10/2010 11:32 PM

Mr. Jahanzeb,

I did not get your cotact phone, any way here is what could be the problem:

1- If the relay was recently put in service the fault could be in A)The wiring from 132kV and 11 kV CT's and/or mis-matched Auxiliary CT's if used. B) Low set Operating Current on the Relay. C) Faulty relay.

2. If the relay was working correctly then the fault could be A) Loose connection/s in the CT wiring anywhere between the CT terminals in the field and terminal blocks at the relay panel and wiring therefrom to the relay terminals.

I could better explain and pinpoint the fault if I had more details which I expected to get on contacting you. Wishing you good hunting.

MIQ

Register to Reply
Member

Join Date: May 2009
Posts: 5
Good Answers: 1
#7

Re: Differential Relays

02/12/2010 4:43 AM

As indicated by a 'Guest' above, Differential Relays should never operate when the fault is outside the Differential Relay Zone. This zone is between the HV terminals of current transformers on all (2 or 3) windings. Current flow in the Trasformer Primary winding is compared with the current flow in the Transformer Secondary/Tertiary windings. Primary and Secondary/Tertiary currents should match and cancell each other leaving a fraction only (10-15% of FL current) and the relay is set to operate at about 30% of FL current. Currents flowing in the Primary and Seconary/Tertiary of the transformer outside this zone should cancell each other leaving the differential relay unoperated. However, a fault within the zone is detected much faster and all feeding sources are tripped in order to limit damage to equipment in the Differential zone.

The above is an attempt to inform you as a layman. I hope you will find the cause and take remedial action soon.

Register to Reply