Previous in Forum: lens   Next in Forum: GATE-2010 (Score Card Calculation)
5 comments
Anonymous Poster
calculate CFM of AHU
02/13/2010 12:03 PM
I WANT TO COUNT cfm OF 20 TON AHU
Re: calculate CFM of AHU
02/13/2010 12:36 PM
You are going to have to provide a lot more information if anyone is to help you.
For starters, what is an AHU?
Charlie don't surf.
Anonymous Poster
02/13/2010 2:42 PM
AHU means Air Handling Unit. This is not a refrigeration unit, whose output is rated in tons. AHU's are made in assorted sizes and their capacity is rated in CFM meaning Cubic Feet per Minute of air. So your AHU has a rating, just as a motor has a rating and a lightbulb has a rating. And it should have a nameplate. And the CFM rating should be on the nameplate. So why not read the nameplate or call the manufacturer and ask what CFM this AHU is rated for. All of this makes the question rather peculiar.
02/13/2010 6:49 PM
The OP needs to clarify. And is the replying guest the same person? If the AHU is rated in tons, it almost surely incorporates refrigeration, and possibly reheat, make-up air, and bypass air among its functions.
In round numbers, cfm = tons × 10,500 ÷ Δt of air.
Anonymous Poster
01/24/2011 10:31 AM
how to find Δt of air????
01/24/2011 10:54 AM
Measure the inlet and outlet air temperatures with a thermometer; subtract.