Diesel Generator Power Factor

02/15/2010 11:57 PM

is it possible to improve power factor of diesel generator by using capacitors.can someone guide me how do i go about.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Feb 2010
Posts: 15
#1

Re: power factor of diesel generator

02/16/2010 1:42 AM

Yes. u can use cap bank but before using it u should know ur reactive power requirements. Also while selecting cap bank cost factor is also imp. U must go for Economical power factor cal . Refer V. K. Mehta's Electrical Power System, S. Chand Publication

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: power factor of diesel generator

02/16/2010 1:44 AM

Yes, this can be done.

The best way to do it will depend on the particulars of your installation. One way is to provide power factor correction capacitors to each of the larger motors. Another way is to provide a bank of capacitors, switched in or out according to the total of motor loads to be corrected.

Some helpful data would include a list of motors with kw or hp for each, the system voltage, and some sample readings of the power factor you are actually experiencing.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 15
#3

Re: power factor of diesel generator

02/16/2010 2:05 AM

U can use this data ...Motor rated output Capacitor rating

2.2 KW (3 HP) 1 KVAR

3.7 KW (5 HP) 2 KVAR

5.5 KW (7.5 HP) 3 KVAR

7.5 KW (10 HP) 4 KVAR

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #3

Re: power factor of diesel generator

01/27/2011 8:02 AM

The value depends on speed too not only on hp. Try to down load from a capacitor or motor manufacturer

__________________
pnaban
Register to Reply
Anonymous Poster
#4

Re: power factor of diesel generator

02/16/2010 7:48 AM

This has been covered earlier also in this forum.

- You do not improve the pf of the generator. You improve the pf of the load and thereby improving the generator performance.

- Thou shouldn't attemp unity pf, stop just short of it, because just by chance the overunity condition leading pf will cause a bit of unstability. No idea about DG, but it is a bit damgerous in big ones.

- Find out the pfs of the load and depending on the size and $ you are ready to spend, go for bank or apfc.

- Please remember there is no hard and fast rule relating load to pf (except incandescant lamps or heaters that are any way almost purely resistive) motor pf widely vary depending on load.

- If you have large generating capacity go for APFC, else based on the pf sample put a bank.

- remember not to overshoot the engine capacity (DG are usually rated at 0.8pf say 1000KVA that means it can give only 800KW, do not assume that at unity pf it will give out 1000KW)

Register to Reply Score 1 for Good Answer
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#5
In reply to #4

Re: power factor of diesel generator

02/17/2010 1:10 AM

Very Good Stuff So Far,

As far as hte Alternator is concerned you need to control the PF of the Load Below Unity. Once the PF Reaches Unity the Control System of Alternator ( AVR ) Malfunctions & raises the Instability of Voltage.

You can have two Options of connecting the capacitor -

Use Capacitor Banks with Auto PF Controller - This will control the PF to the Preset Value by Switching On & Switching OFF the Capacitors depending upon the Load Amp & Load PF.

Secondly you can have localised Capacitors installed between the Motor Starter & the Motor- This capacitor will come in Circuit when you start the motor, Otherwise this will be disconnected from the system.

Please remember - The Capacitors should not be connected to the Alternator When the Alternator is running on No Load, This will Make AVR of the Alternator to Malfunction & will work in Instable Zone.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2010
Posts: 14
#6
In reply to #5

Re: power factor of diesel generator

02/18/2010 12:51 AM

thanks for responding.

are their any chances of reduction in diesel consumption and how much percentage

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: power factor of diesel generator

02/18/2010 5:48 AM

Minimal
What is your actual power-factor (uncompensated?)
The reactive power also called imaginary power is acually imaginary power. The Engine does not supply it. It is only what is exchanged between various line components.
While exchanging, it creates certain additional line losses, that is the only thing you can save.
In case of short lines, with proper cabling (size), the cable resistance will be low enough to make the extra I2R loss negligible.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abhishekkatkar (2); Anonymous Poster (2); pnaban (1); shekhar kadam (1); Tornado (1); vishram lele (1)

Previous in Forum: Motor KW Increased   Next in Forum: Conduit Selection

Advertisement