Cable Sizes

02/17/2010 7:26 AM

Load = 500Kw

length= 1 Kmeter

voltage= 400V

Barried by about 1meter

3phase

what is cable suitabe size can use

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: cable size

02/17/2010 11:11 AM

Try this. Keep in mind that these calcs are NEC. Don't know where you are.

http://www.electrician2.com/calculators/wireocpd_ver_1_parallel.htm

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: cable size

02/17/2010 12:19 PM

Lets see a little effort from you.

Amp load = 500 kw/(0.400v x 1.73 x PF)

Check your code book for conductor that has this ampacity or greater.

Using the amps and conductor impedance calculate voltage drop

If VD is too high use a larger conductor.

Post your results so we can help.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Feb 2010
Location: Mongolia
Posts: 1
#4
In reply to #2

Re: cable size

02/18/2010 9:56 AM

How to choose cable size? What is VD?

__________________
Life is fun.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cable Sizes

02/18/2010 7:50 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Cable Sizes

02/18/2010 11:51 AM

Dalai Quote "How to choose cable size? What is VD?"

This may be beyond you capability. You look in the applicable code book for you area for the conductor ampacity. Choose the conductor based on its ampacity or use the British Standard 7671. VD is voltage drop. It looks like you need some technical assistance beyond this forum

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2010
Posts: 15
#6

Re: Cable Sizes

02/19/2010 6:46 AM

Dear,

Your demand is unreallistic. Ur system current is 1137Amps. So there is no cable available according to ur requirements. Better way to change ur vtg level or use power distribution board and distribute ur load.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Cable Sizes

02/20/2010 8:28 PM

abhishekkatkar Quote "Ur system current is 1137Amps. So there is no cable available according to ur requirements"

You need to check you calculations again. We don't know the PF but if it is unity the load is 723 amps. Ever heard of using parallel conductors? I am not used to using metric sized cable but 150 mm² = 380 amps x 2 = 760 amps. Is this not available?

Register to Reply
Anonymous Poster
#8
In reply to #7

Re: Cable Sizes

02/21/2010 3:28 AM

pf=90

and we need to use 4 core cupper armured cable

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 15
#9
In reply to #7

Re: Cable Sizes

02/21/2010 8:03 AM

thanks.i got it.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#10

Re: Cable Sizes

02/21/2010 6:25 PM

1000 meters is too far. You will need to transform up to a higher voltage. If you use 4 KV, your load is about 100 amps and you can use a much smaller cable, something like 25 mm². Check you local code for the ampacity.

Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!