Busbar Rating

02/17/2010 11:44 PM

Hai,

i am working in oil and gas industry as electrical projects engineer.

we have 415V panel in which bus bar rating is 50kA(i think this is Symmetrical rms value).We are doing Short circuit study for that network where symmetrical SC values for 3Φ fault are below 50kA.but assymmetrical values are about 61kA.

Now my doubt is "Is the panel is ok or any problem.How to find assymmetrical rating of busbar".

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#1

Re: Gopi

02/18/2010 12:57 AM

In all cases, symmetrical ratings are calculated and then this value is multiplied by suitable factors to get the asymmetrical value. You can search in Table No-8 of NEMA standard. This factor is as per X/R ratio at SC point.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Busbar Rating

02/18/2010 12:13 PM

If the panel rating is above the symmetrical fault then it is usually adequate for the asymmetrical value. Verify this with the MFG.

Reply Score 1 for Good Answer
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Busbar Rating

02/18/2010 11:14 PM

With a 50kA symmetrical fault level, as per IEC, the asymmetrical peak withstand should be 105kA peak. This usually lasts only a couple of cycles, so the key thing is that the busbars, supports etc must withstand this. Whenever i had to do these withstand tests at the test lab here, i used to apply 5 cycles with the asymmetrical peak of 105kA, followed by a 1 sec test without any asymmetry. This way, you can find out whether any failure is due to dynamic effect or thermal effect.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Reply to Forum Thread 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

kvsridhar (1); sidhu16 (1); wareagle (1)

Previous in Forum: LV Distribution and Location of Electrical Room   Next in Forum: Cycloconverter

Advertisement