If i placed three toroid CTs in three different phases of voltage rating 220volts. is it possible to connect the output of these CTs in series? what happen in this condition?
If this possible then where should we connect the current indicator and what will it measure(right current or not)?
Re: Current Transformers in series
02/18/2010 10:26 AM
It is possible to connect them in series, but the output would be zero (unless the currents in the three phases were not equal).
02/18/2010 11:19 AM
This is the principle of RCD (provided you have folowed the correct sequence).
The phasor sum of 3 currents (balanced or unbalanced) should be zero - KCL-unless some current leaks out.
Re: Current Transformers in Series
02/19/2010 4:00 AM
If it is balance system you will defenitely measure zero on your current indicator, unless ther is a leakage current.
Dan Segami
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member
02/19/2010 4:16 AM
You actually get no output current from this connection. If there is any mismatch between CT's then you can have few leakage currents.
02/19/2010 6:27 AM
If its a delta system (3 WIRE) it should be zero. If its a Y (3 phases + neutral) you should get the save value as one CT on the neutral line.