Maximum Possible Size of Downstream Transformer

02/18/2010 2:06 PM

Dear All,

I need advice on the following issue regarding power transformer.

Up stream voltage: 132KV

Down stream voltage: 11KV

MainTransformer rating: 25MVA

Max Existing load:10MVA

I need to connect in the down stream a new transformer of 9 MVA,11KV/6.6KV for connecting SQCI motors.

Is it possible to operate on the existing system. will the main transformer support when we switch on the 9MVA transformer.

I can switch off some existing loads if required.

I will be very thankful if some body can advice.

best regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Maximum possible size of down stream tranformer

02/18/2010 3:46 PM

I don't see any issue with doing this.

Just ensure:

The primary and secondary cables of transformer, 11 KV bus and other related gears are rated for the additional load (it should be designed with the full capacity of transformer, but in case)

The transformer protection settings are adequate to avoid nuisance tripping with additional loads (I would suggest to do the relay coordination study)

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Maximum Possible Size of Downstream Transformer

02/18/2010 5:40 PM

The 25 MVA transformer is not a concern.

1. Can the 132 KV system take the added load.

2. Are the 11 KV conductors large enough for the added load? Voltage drop?

3 11 KV breaker ampacity.

4. Effect on other customers? Motor Flicker?

5 Does the Fuse on the 9 MVA transformer coordinate with the feeder breaker?

6 What did I forget?

Reply Score 1 for Good Answer
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#3

Re: Maximum Possible Size of Downstream Transformer

02/20/2010 10:30 AM

My Friend,

Do what MSAMAD recommendations and add the "voltage dip" protections from the largest capacity/rating of the SQCI motor(s) to complete your system protections.

Eren

Reply
Participant

Join Date: Dec 2008
Posts: 3
#4

Re: Maximum Possible Size of Downstream Transformer

02/24/2010 10:31 AM

Dear Freind..

We have to check the starting current of the Motor

Reply Off Topic (Score 5)
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ereneduarte (1); msamad (1); muttu9@yahoo.co.in (1); wareagle (1)

Previous in Forum: Current Transformers in Series   Next in Forum: Heaters on One line Diagram

Advertisement