EHV Transmission

02/21/2010 7:13 AM

We have a 110KV Double Circuit transmission to our Main Receiving Sub-Station where Voltage is reduced to 110KV/11KV. We have Bus coupler both at 110KV side and 11KV side. Both the supply are tapped from the same bus at TNEB sub-station. Now to have redundancy in supply due to failure of one of the lines, whether we can close both the 110KV and 11KV bus couplers. What should be the protection available in the bus section and the feeders for this application.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#1

Re: EHV Transmission

02/22/2010 2:08 AM

You can have distance protection Schemes at your end as provided at th TNEB Substation, so that the faulty feeder alone tripped on Both ends, leaving the healthy feeder to feed to your loads.(/p)

If numerical relay protection is used, you may have to enable parallel feeder protection settings additionally for correct operation of protection System,

Both bus section isolators can be kept closed, If one feeder is capable of handling your total load.

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Associate

Join Date: Oct 2006
Location: Hyderabad,India
Posts: 49
#2

Re: EHV Transmission

02/24/2010 11:51 AM

Dear Sir

Pl clarify the following:

1) If both the supplies are from the same section on 110 kV side then where is the question of having a buscoupler in between ?

2)How many incomers does the 11 kV switchgear has?If you are planning to close the buscoupler then u may have to defeat mechanical and electrical interlocks(which might be detrimental to the equipment/personnel) to close the buscoupler.

3)If you are closing the buscouplers (assuming the supplies are being derived from either side of the buscoupler ) on the EHV side(may not be under your control,since u are telling it is TNEB substation) and HV side you might actually be paralleling the sources,which would result in catastrophe, in the event of a fault on any one of the involved lines.

4)However, the distance protection /OC/EF are available to isolate the fault.Nevertheless it is risky and not recommended in SOPs.

Regards

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#3

Re: EHV Transmission

02/26/2010 5:50 AM

Switch off the both breakers of failed feeder. Now put ON the 11KV B/C only.

Your live feeder can be protected by Directional O/C-E/F and other Trf protection with Partial Differential and LBB.

Register to Reply