Generator +ve Sequence and Zero Sequence Impedance

02/21/2010 11:00 PM

can we find the positive sequence [X,R] and zero sequence impedance [X,R] from the data generator given ? :-

X/R ratio = 10
MVA = 100
kV =132kV
Fault level = 7200

i'm only get to find their generator sub-transient impedance Xd" by this formula :-

generator fault level (MVA) = generator capacity (MVA) / generator subtransietn impedance (Xd")

we can get their Xd" = 1.39%... after that i dont know how to continue their calculation..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: +ve Sequence and Zero Sequence Impedance of Generator

02/22/2010 11:58 AM

Homework?

Register to Reply
Participant

Join Date: Oct 2009
Posts: 4
#2
In reply to #1

Re: +ve Sequence and Zero Sequence Impedance of Generator

02/22/2010 8:46 PM

nope.. now i'm doing protection study at one of heavy industry in malaysia.. from the study, it must validate with the calculation.

fyi, i have found to solve the zero impedance by this formula :-

Xs(0) = (3 X Base MVA / 1p fault MVA) - 2 Xs(1)

and the problem, i'm do not have data of 1p fault MVA (single phase).. huhuhu..

Register to Reply