what happends when you lose a phase (i.e) blown fuse or something similar
in a wye connection in a line side and what happens when you lose a phase in the load side of a wye?
Re: Phase Loss
02/23/2010 6:06 PM
Re: Phase Loss
02/24/2010 2:56 AM
On a supply to a motor, expect either the motor overload protection device or the circuit protection device of one or both of the other two phases to operate as well.
Re: Phase Loss
02/24/2010 11:39 AM
Single phasing takes place. Should the load be a motor, it will stop rotating and "hum" until the o/l trips. In a resistive load i.e. lighting situation, some lights will be out.
Good Answers: 244
Re: Phase Loss
02/24/2010 1:52 PM
The previous thread http://cr4.globalspec.com/thread/40007 will also help.
- MS
Re: Phase Loss
02/24/2010 7:58 PM
thanks guys