Phase Loss

02/23/2010 2:37 PM

what happends when you lose a phase (i.e) blown fuse or something similar

in a wye connection in a line side and what happens when you lose a phase in the load side of a wye?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Phase Loss

02/23/2010 6:06 PM

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Phase Loss

02/24/2010 2:56 AM

On a supply to a motor, expect either the motor overload protection device or the circuit protection device of one or both of the other two phases to operate as well.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jan 2010
Posts: 8
#3

Re: Phase Loss

02/24/2010 11:39 AM

Single phasing takes place. Should the load be a motor, it will stop rotating and "hum" until the o/l trips. In a resistive load i.e. lighting situation, some lights will be out.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Phase Loss

02/24/2010 1:52 PM

The previous thread http://cr4.globalspec.com/thread/40007 will also help.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Participant

Join Date: Feb 2010
Posts: 2
#5

Re: Phase Loss

02/24/2010 7:58 PM

thanks guys

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jannel (1); msamad (1); PWSlack (1); w0148360 (1); wareagle (1)

Previous in Forum: Motor Protection Relay (MPR)   Next in Forum: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system
You might be interested in: Fuse Holders, Power Transformers, Over-the-Side Heaters

Advertisement