Determining the Pipe Invert Level

02/23/2010 2:56 PM

Hi there!!

How to find the the Invert level?? I have 2 manholes the one has IV level 1.5m , the pipe size is 200mm and the distance between 2 manholes is 20mtr.. slope 1:100. how to find Invert level of the 2nd manhole?? thanks!! the slope of 1:100 is correct??

Thank you!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: How to find the invert level of a pipe?

02/23/2010 3:43 PM

Hello,

Pipe diameter will have no influence in the outcome since the invert is the "inside surface of the bottom of the pipe".

1:100 across 20m gives 0.2m fall from one manhole to the next. Thus relative to the original manhole the next one will be 200mm lower.

However, you will need to adjust for the soil surface "slope" or contour condition unless you can survey back to the same datum.

By the way, check the calculations. It may be different if the 20m is from (centre to centre) or (edge to edge) and where in the manholes the invert levels were taken.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Location: Calgary AB
Posts: 21
Good Answers: 2
#2

Re: Determining the Pipe Invert Level

02/24/2010 10:44 AM

Just an engineer said it exactly. But I felt the need to add a pedantic methodology for you

Open the second manhole.

You have measured from the rim down to the invert on the first manhole and found it to be 1.5m. If the elevation of the second manhole rim is exactly the same as the first, AND the pipe installer managed 1:100 on the pipe, then the second invert will be 1.7m below the rim (if the end to end measure on the pipe is 20m, and not center to center of the manholes).

This is usual practice to 'as-built' a site (but doesn't address pipe sag).

That being said, if you determine the manhole elevations (by survey) and find the invert fall to be different than 200mm, you don't have what you thought.

Never assume what was on paper exactly matches what was built.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#3

Re: Determining the Pipe Invert Level

02/25/2010 9:36 AM

I agree with the posters. Is this existing or proposed? Is the line to carry storm water or is it a sanitary line? If sanitary, a 1% slope doesn't seem to be enough to keep the solids flowing.

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Determining the Pipe Invert Level

02/25/2010 11:16 AM

You're wrong. One-percent is quite steep. A 12-inch concrete pipe sloped at 1 percent will have a velocity in exceess of 4 fps (by Manning's equation).

A velocity of 2 fps is required in wastewater to prevent settling.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#5
In reply to #4

Re: Determining the Pipe Invert Level

02/25/2010 11:36 AM

Sorry guest. I don't design sanitary sewers. My experience is from designing network undergound ductline. We always shot for 2% slope to be sure there was no buildup of silt in the ducts.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Just an Engineer (1); NoEngr (2); rjyou (1)