MECHANICAL AND ELECTRICAL LATCHED VACCUM CONTACTORS

02/24/2010 11:11 AM

Hello Experts,

I am a fresher,just out of college,joined an organization recently.In our plant there are two kind of vaccum contactors used for feeding H.T motors,one is mechanically latched and other is electrically latched,i could not get the answer ,please somebody help.

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: MECHANICAL AND ELECTRICAL LATCHED VACCUM CONTACTORS

02/24/2010 11:38 AM

See the answers:

Mechanically latched contactor:

There are two springs used in this system: one is closing spring and the other is tripping spring. The closing spring is stronger than the tripping spring. Once the breaker is closed, a mechanically latched system holds the breaker in closed position. When the contactor needs to be opened, the latch is released by the tripping coil. For detail mechanism, see the previous thread: http://cr4.globalspec.com/thread/39932

Electrically latched contactor:

In this mechanism, the contactor is held at closing position by an electrical Holding coil. As long as the holding coil is energized, the contactor remains closed (against tripping spring). When the contactor needs to be opened, the holding coil is de-energized and the contactor is opened with the action of the tripping string. There are two categories of this type of contactor: (1) the first category has single closing coil which is used for both closing and holding, all small size and low voltage contactors fall in this category, (2) the other category has separate closing coil and holding coil. Closing coil is stronger than holding coil. Once the contactor is closed by the closing coil, it is latched by the low power holding coil. Larger size and medium voltage contactors fall in this category. Generally DC power is used for the energizing coils.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: MECHANICAL AND ELECTRICAL LATCHED VACCUM CONTACTORS

02/24/2010 11:39 AM

An electrically latched relay or contactor is held in the actuated position by maintaining power to its coil, typically via an auxiliary NO (normally open) contact. The coil consumes a small amount of power and generates a small amount of heat.

A mechanically latched relay or contactor has two coils. With a brief signal, the actuating coil operates the relay, but then the relay stays in the actuated position until the deactuating coil (brief signal again) turns the relay back "off." Neither coil is energized for very long; this minimizes power usage and heat generation.

[Note, that should be "vacuum", not "vaccum". The concept applies to regular contactors as well as vacuum contactors.]

(Sorry to be redundant, but msamad must have posted just as I was writing this. My apologies for the near echo.)