Load Cell Output

02/25/2010 6:01 AM

Load cell is sized at 200kg rated capacity with 2.00mV/V output, what does the output mean per kilo?

We are using 4 load cells in paralell on a weigh conveyor system so output is divided by 4, ie 0.5mV/V. Conveyor weighs 550kg. Range of weight on conveyor is 0.2 to 20kg. Cannot read outputs below 0.5kg. Are we below the minimum resolution of the system? ie 0.5kg in 800kg

__________________
A day without a smile is a day lost
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Spain - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Oct 2007
Location: Madrid, Spain
Posts: 716
Good Answers: 25
#1

Re: Load Cell Output

02/26/2010 2:17 AM

Hi,

Output of any load cell, given in mV/V means the mV output per V excitation at full scale loading. In your case, you will have 2/200 = 0.01 mV/kg signal per V excitation, if your excitation is, for example, 5 V then you will have 0.05 mV/kg signal.

The resolution of the system normally is not limited by the load cell, but the electronic bridge conditioning/measuring device.

Which are the specifications of the bridge conditioning device?

Kind regards

__________________
It's stupid to discuss about AI: We´ve reached by the "B" way. We' ve producing men as clever as machines.
Register to Reply
Guru
Engineering Fields - Control Engineering - Time to take control United States - Member - New Member Engineering Fields - Systems Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Apr 2009
Location: Tampa, Florida, USA
Posts: 2129
Good Answers: 87
#2

Re: Load Cell Output

02/26/2010 2:31 AM

The output voltage will be 2.00 mV at the rated load, 200 kg, for every volt of supplied to the load cell.

For instance if the power supply to the load cell is +5 Volt, then a 200 kg load on the load cell will give an output of 10 mV (5 V * 2 mV/V). So the scale factor from kg of load to voltage output of the load cell would be 10 mV/200 kg or 0.05 mV/kg.

If you are using the load cells to measure 550 kg + 0.2 kg up to 20 kg, then your total load varies between 550.2 kg and 570 kg. Without knowing the geometric distribution of the load it's difficult to say how much load will be on each load cell. Regardless the load cell should be able to measure loads down to zero kg. And if the load is poorly placed (meaning more than 200 kg of the load is over one load cell), then you may saturate the load cell output.

How are you reading the output? With an analog volt meter? Or do you have some sort of digital read out? If it's digital, then there's a good chance the limitation is in the electronics or the software providing the display.

__________________
J B
Register to Reply
Participant

Join Date: Feb 2010
Location: Soria (Spain)
Posts: 3
#3

Re: Load Cell Output

02/26/2010 3:14 AM

My experience is to use a box of addition, it supplies 10V exactly and adjustable to each cell and also adds the mV of each cell, obtaining a single signal in mV in all cells.
Moreover you must know the recommendation to use, if possible, only three cells. A weight is supported on a plane, a plane is defined by three points. With four, maybe a cell instead of weight-bearing, whether it is subject to the charge, is being stretched, so it shows 0 mV, but the other three show more weight than real.

Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#4
In reply to #3

Re: Load Cell Output

02/28/2010 12:02 PM

Wrong! If cells have SAME sensitivity ALWAYS the sum of outputs will be the load which ever is the load position.

This is obtained by a calibration in situ of the load cells+conditioners by placing e load in different KNOWN positions. Depending on obtained (displayed) results corrections are made for each load cell acquisition line till result INDEPENDENT of load position.

I made weighings up to 3.000 T with such calibrated load cell groups (4) and results were able to show that weight is an invariant!