What would be the typical EFF and PF for motors when doing a conversion? I found this.. but I'm not sure if its valid
1HP=746 watts.
HP=IxVxPFxEFF/746,where PF( Power Factor)=.86 and EFF ( Motor Efficiency)=.81. Using this formula current can be calculated as follows for a 1HP single phase motor.
-Jim
Re: Conversion to HP for motors?
02/26/2010 2:30 PM
EFFICIENCY= POUT/PIN= 746/PIN
PIN = 921 W
PIN = V I COS (ANGLE)
COS (ANGLE) = PF =0.86
CURRENT= 921/V* PF
Your formula is correct.
Re: Motor HP Conversion Formula
02/26/2010 11:35 PM
I am not a practising electrical engineer and while my first impression was that your formula was correct, however it occurs to me that you may be double counting.
As you might know, apparent power is V xI but real power is V x I x PF where V = Volt, I = Current and PF = Power Factor. Efficiency is "power out"' over "power in" expressed as a percentage. It follows then that if the "power in" figure was apparent power (and I would think this was the most common used definition), then the efficiency term would already include an allowance for "PF" , and including it again would be double counting.
02/28/2010 8:28 AM
The formula is correct and an allowance for power factor is needed, as shown in the formula. Efficiency does not take power factor into account.