Why are Electric Meters Grounded Street-Side?

03/01/2010 9:07 AM

I live in a suburb of Chicago where homes were built with the usual grounding on the house side of the meter. Now when selling or buying a home here the city inspector requires that the meter be grounded on the street side. what is the reasoning for this? doesn't the bare or neutral wire coming into the house act as a ground back to the generation site?

oilcan13

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#1

Re: Why are Electric Meters Grounded Street-Side?

03/01/2010 12:46 PM

hi,

why don't you ask him (the city inspector) directly?

__________________
Just live and .. Learn!!
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Why are Electric Meters Grounded Street-Side?

03/02/2010 5:34 AM

The City Inspector probably doesn't know the actual reason. He just knows that the city changed it to this way and so he makes sure its done this way.

I've only met a couple of City inspectors in my area that actually have any clue to why things are done the way they are done.

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#5
In reply to #2

Re: Why are Electric Meters Grounded Street-Side?

03/02/2010 9:16 AM

See above answer.

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#4
In reply to #1

Re: Why are Electric Meters Grounded Street-Side?

03/02/2010 9:15 AM

They Point out its in the code. In other words, "not for Me to reason why"

Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#3

Re: Why are Electric Meters Grounded Street-Side?

03/02/2010 7:38 AM

In answer to the first part of your question, see the first two answers.

In answer to your second part of the question, the utility company serving you is a separately derived system, owned and maintained by the utility company. It has its own rules, codes and regulations (for very good reasons). The short answer would be: Yes it is properly grounded.

There is a reason to isolate the power company ground from the building ground. Mostly feedback power on the ground from the utility company because of failure or lighting. For more detail I recommend Soars Grounding Book.

In conclusion, this is not the first time I have heard an inspector or other people confused about how a building should be grounded. This area is a de-mark of where the utility company ends and where your ownership begins. Eventually someone will point out the problems with his recommendation and it will go away.

Register to Reply