APC 5000 UPS

03/04/2010 4:24 AM

i have a APC 5000 ups that is not working properly i have found that its batteries are not charging. what will be the solution?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: APC 5000 UPS

03/04/2010 8:20 AM

What is the history of the UPS? Age, frequency of use, length of use at each outage. What does the batt pack read when disconnected? What is the charge output? Sorry to answer questions with questions but that's how we try to get you up again.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: APC 5000 UPS

03/04/2010 5:58 PM

Most probably it is defective battery.

Battery cells are connected in series within the battery and the batteries themselves are connected in series within a battery bank. If any of the cells are defective, the series connections are broken and the battery will not be charged and/or delivered power. This is one of the major disadvantages for having multiple batteries connected in series. You didn't mention your DC voltage range; I am guessing you have more than 12V DC system and multiple batteries connected in series. If this is the case, check each of the batteries and replace the defective one.

If the batteries are too old, better to replace the complete battery bank.

- MS