DG Neutral and Body Earthing

03/05/2010 2:04 AM

Why it is said that one should have separate earth pit for body earthing & neutral earthing of DG set & these pits shall not be connected to same earth grid?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: DG Neutral and Body Earthing

03/09/2010 9:33 AM

Why only Neutral and body earth pits? As per National and international standards, all earth pits - I repeat - ALL earth pits in the plant premises MUST be linked/bonded, including Transformer Body, transformer Neutral, HV Body, Equipment Body, Lightning Protection earthing, Electronic earthing, static earthing - you name it, all must be connected together.

Register to Reply
Associate

Join Date: Jan 2010
Location: Singapore
Posts: 26
#2
In reply to #1

Re: DG Neutral and Body Earthing

03/09/2010 11:07 PM

It will be very kind of you, if you can specify IEEE or IEC standard where it is written so.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: DG Neutral and Body Earthing

03/10/2010 8:14 AM

Vide Cl. 9.10.12.2 of IEEE 1100, "the use of any separate, isolated, insulated, dedicated, clean, quite, signal, computer, electronic or other such improper form of earth grounding electrodes for use as a point of connection of the EGC (Equipment Grounding Conductor) is not recommended".

And… vide Cl. 5.5.4.5 of IEEE 142, 'The NEC requires that all equipment served from an electrical source be grounded or bonded to the grounding point of that source. In addition, neutral of all power supplies are required to be grounded. Clearly, when an isolated grounding electrode is used for a computer, this violates NEC requirements. The NEC requires a metallic path from all equipment frames served, back to the source neutral".

vide IEC 60364-7-707: The use of independent, "isolated" earth electrodes for computer or

electronic systems is not recommended/

permitted.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#4
In reply to #1

Re: DG Neutral and Body Earthing

03/21/2010 5:29 AM

They can/must be linked underground,but should be seperate pits for body & neutral earthing.Connecting strip from body & neutral should go to respective earth pits.Isn't it right?

__________________
"Know something about everything and everything about something"
Register to Reply