Dear all,
I would like to know the following :
There is a tertiary delta winding in 230/132 KV auto transformer in the grid sub-station. What is purpose of that tertiary delta winding in transformer? Please explain.
Thanks.
Rashid
Re: Purpose of tertiary winding in power transformer
03/05/2010 12:01 PM
In the case of large transmission autotransformers, which must of necessity be star/star connected, a common use of the tertiary winding is for connection of system compensation equipment.
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member
Re: Tertiary Windings in Power Transformers
03/05/2010 11:57 PM
The main purpose of tertiary windings-
1. To eliminate or reduce the harmonic component and keep system healthy.
2. To protect it from neutral shifting.
3. Some time, it supply auxiliary loads.
Good Answers: 170
03/09/2010 8:50 AM
Normally such tertiary is Delta connected; this is to provide a circulating path for zero sequence currents.