Setting of turbine rotor float

03/06/2010 1:39 PM

If i have rotor float of 0.25mm and i set XT at zero at 0.125mm so that rotor can move only 0.125 towards active side, what was wrong if the value of XT shows 0.2mm when the rotor was in running condition. Why the value exceeds beyound the maximum set value?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Setting of turbine rotor float

03/07/2010 12:00 AM

Float check and zero setting are done when the rotor is in stationary condition. If there is face-out in the thrust-collar, (though possible) it is difficult to make out during the 'float check'. This existence of 'face-out' would make a different reading while running from that set condition. Face out could be a local problem of thrust-collar or due to a bend in the shaft (which developed on the run due to reasons like imbalance).

Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#2
In reply to #1

Re: Setting of turbine rotor float

03/07/2010 12:02 AM

Float check and zero setting are done when the rotor is in stationary condition. If there is face-out in the thrust-collar, (though possible) it is difficult to make out during the 'float check'. This existence of 'face-out' would make a different reading while running from that set condition. Face out could be a local problem of thrust-collar or due to a bend in the shaft (which developed on the run due to reasons like imbalance).

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Anonymous Poster
#3

Re: Setting of turbine rotor float

03/07/2010 3:43 AM

The XT reading fixed during assembly of Thrust bearing always increase during operation. It is very rare when there is no increase in set value. There are three main reasons:

1. Thermal Growth of Rotor

2. Springness effect on operationg loads

3. Residual run out of collar

In my point of view XT reading of + 0.20 mm is quite normal provided it is stable and bearing babbitt temperatures are less than 95 celcious.