Steam Pipe Line

03/06/2010 10:03 AM

dears,

we have power house of 10 MW, the boiler is 100 Tons/Hr. and Turbo Alternator is 10 MW. the steam specification is as:

Turbine inlet pressure 62 Bar g

Steam Temperature 480 deg C

distance between Turbine & boiler is 90 Meter.

please suggested me, what is the specification of steam pipe line between Boiler to Turbine? for 62 Bar and 480 deg. C supper heated steam.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Steam Pipe Line

03/08/2010 3:26 AM

What size is it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2008
Posts: 25
Good Answers: 1
#2

Re: Steam Pipe Line

03/08/2010 4:13 AM

Hi aligillani,

The specification that governs the piping design is:

ASME B31.1,power piping.

herein a quick selection guide:

ASTM SA-335,Grade P11 for design temperature less than 510 degree cent.

Grade P22 ( 2 1/4 Cr ) for temp.between 510 and 566 deg. cent.

Grade P22 for temp. between 510 and 574 deg. cent. in the DN 150 and smaller size range.

Grade P91 for temp. between 538 and 593 deg. cent.

Regards,

Sayed

Register to Reply
Anonymous Poster
#3

Re: Steam Pipe Line

03/08/2010 4:48 AM

Let us understand- you are working in superheated steam over 90m length and you don't know the pipeline specification (i presume it is the material you want) -

With all due regards, don't try to guess these areas. The ASME PV is highly specialised area. get hold of some consultant who is qualified to do the design. The material of the pipe is only one, small, part of the pipe line.

I can list out factors that will have the effect - and that may not only have on material , but on schedules too, to certain extent.

Register to Reply
Associate

Join Date: Jan 2009
Location: Saudi Arabia
Posts: 39
#4

Re: Steam Pipe Line

03/08/2010 11:44 AM

Get help from an expertises in steam pipeline, it is impractical to do this by your self

Register to Reply
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#5

Re: Steam Pipe Line

04/26/2020 6:43 AM

Dear Mr. aligillani,

Your point is what is the material specification for of steam pipe line between Boiler to Turbine? for 62 Bar and 480 deg. C supper heated steam. You have not mentioned about the turbine house, position, and total length is it horizontal length or inclusive of bends and if bends are included how many etc. to be taken in to account.

It is not the specification alone to be noted. Even if you know the specs. the steam pipe lay out design is not simple as if it is water line. The FLEXIBLITY ANALYSIS is to be made since the Thermal Expansion of the pipe material and its resultant forces to be analysed, and thermal expansion will be considerable level for the temp. and length you have mentioned.

Assuming the ambient temp. is 40 Deg.C for a length of 90 Metres the pipe expansion will be about 285 MM in total, (11.22 Inches) and this expansion to be taken care with proper expansin loop, bends supports and anchoring etc., If expansion loop is accounted the total pipe line length will be more than 90 Metres.

Further the Turbine Manufacturer must have given the maximum Forces and Bending Moment allowable on inlet flange and exhaust flange and this is to be done properly which is a specialised job.

Hence my suggestion is mere knowing specs alone is not sufficient. Do not take risk as the safety is prime consideration for the equipement and staff. Do not think you are being discouraged.

Dhayanandhan.S

__________________
DHAYANANDHAN.S
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#6

Re: Steam Pipe Line

04/26/2020 10:44 AM

You have some very good advice stated above....

I have been involved with the specification, design and analysis of piping systems for over 40 years. The engineering and analysis of Superheated Steam piping systems is at the top of difficulty of Piping engineering and is certainly no place for a beginner to learn. Designing the correct piping supports for such a high energy systems is a separate and not insignificant challenge

Spend the money and engage the services of an experienced professional for your powerplant high energy systems..... Despite what an MBA might tell you, do not assign a young fresher just out of the University.

I have another issue with material selection ...

I would not use or specify the ancient ASME SA 335-P11 (low alloy material) for this system. P11 has a forty year history of catastrophic failure when supplied in an axially seam welded configuration. Use the higher alloy P22 material in the seamless condition (which gives you margin on slightly higher temperature usage) .... It will be nearly the same cost.

The P22 will protect you against the inexperienced boiler operator who will accidentally (ooopps!) run the boiler above its design temperature.

The P91/P92 materials are also acceptable, but are more expensive and difficult to weld into place.

Good luck ....Please tell us more about your project and do not be afraid to continue to post questions...

Regards

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#7
In reply to #6

Re: Steam Pipe Line

04/27/2020 2:48 AM

Thank you Mr. MJCronin for your observation on my above posting

Another important issue is (though the original post did not ask for ) is the STEAM LINE BLOW-OUT and conclusion on the observation of Target Plate. This subject does not get the due importance and attention for the proper support for new steam line blowing-out and I am the witness for a case where support has failed and caused problem.

Luckily no injury to anybody or serious damage except a bend totally damaged near the turbine side or else the twist and swing, due to reactive force, could have damaged the turbine governor and shattered to pieces and a fatal blow to near by staff.

The narrow escape was due to just a gap of 12 MM between the governor and pipe swing path and no staff with in 10 feet distance, while the bend swing was 180 degrees. This happened 43 years back, and in those days to get a new turbine governor will need minimum 8 months.

Incidentally what was the practise of pressure for line blow-out and criterion for the target plate you have followed - is it for the full working pressure and temp. or less than that. I insisted on full working pressure and temp. and cleared the target plate blow of less than 10 dents of 0.2mm size for 3 consecutive blows.

Thanks,

DHAYANANDHAN.S

__________________
DHAYANANDHAN.S
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#8
In reply to #7

Re: Steam Pipe Line

04/28/2020 5:24 PM

A good, but somewhat dated summary of HP steam piping system design is contained in "The Piping Handbook" by Nayyer (Chapter C3 and B4 B5).

The governing code for these steam systems is typically ASME B31.1

Generally speaking, each and every pipe support on these systems requires detailed engineering as well as periodic re-adjustment after system shake-down.

There should be some evaluation of steam system transients "Steam Hammer" due to rapid valve closure.

After installation, there should be a detailed periodic inspection plan developed for the Main Steam and other High energy piping systems.

Again, high energy piping system design is not for beginners .....

Tell us more about your system

- Are allowable loadings on nozzles a consideration ?

- Do you have a piping layout with pipe support locations determined ?

- Do you have safety/relief valves on your system ?

- What is your code of record ?

__________________
We have met the enemy....and he is us. POGO
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#9
In reply to #8

Re: Steam Pipe Line

04/29/2020 8:48 AM

An excellent background document about boiler and steam systems:

https://portal.endress.com/wa001/dla/5001084/9862/000/00/CP01195DEN_0117.pdf

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#10
In reply to #9

Re: Steam Pipe Line

04/30/2020 3:11 PM

This document explains some of the subtlties and important design issues related to steam piping hanger design.

Remember, the hanger components that touch the high temperature steam piping must also be designed to operate at the high temperatures.... i.e. alloy materials are required.

https://s3.amazonaws.com/s3.anvilintl.com/resources/literature/PipeHanger_DesignEngineering_Catalog.pdf

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#11
In reply to #10

Re: Steam Pipe Line

05/01/2020 12:18 PM

According to some preliminary estimates I have made, based on your 100ton/hr massflow rate, pressures and temperatures, your system is probably 10" or 12" NPS and schedule 80....

Again, this is PRELIMINARY, because you have either lost interest or stubbornly refuse to give us any more information...

Based on this sizing and pipe schedule, you should probably select the ASME SA335-P22 alloy steel material. Your modest massflow and relatively low design temperature does not justify the extra capital and installation cost of the higher alloy P91/P92 piping material.

It is too bad that there is no more interest in this thread. High temperature piping design is certainly an important and interesting engineering topic that seems to be slipping into the sands of time .....

__________________
We have met the enemy....and he is us. POGO
Register to Reply
2
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#12
In reply to #11

Re: Steam Pipe Line

05/11/2020 11:06 AM

Pipe supports and Spring Hangers on steam piping system require an extra level of detail and care.

High-temperature spring hangers are commonly specified as "constant supports" rather than variable spring hangers. This is done to ensure that piping stress levels are kept within a tight range.

High temperature piping Spring hangers must be designed to ensure that in-situ periodic adjustment and testing is possible. These measures are NOT necessary for most other piping systems

http://www.fastorq.com/wp-content/uploads/Pipe-Hangers-Piping-Loads-Section.pdf

Additionally, long horizontal runs of high temperature piping are sometimes susceptable to dangerous mid-span "sagging". This sagging is dangerous because it can allow condensate build-up and a phenomenon known as "steam hammer". The high temperature and reduced elastic modulus of piping materials allows this sagging that would not exist in lower temperature piping systems.

In other words, the competent and careful piping designer must consider requiring a more aggressive piping slope for a high-temperature steam system than for a low temperature steam system.

There are other very important design considerations that must be considered for these challenging and dangerous steam systems ....

__________________
We have met the enemy....and he is us. POGO
Register to Reply Good Answer (Score 2)
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#13
In reply to #12

Re: Steam Pipe Line

06/10/2020 11:05 AM

Thank you Mr. MJCronin for your valuable inputs on this topic. I hope the original poster has taken note of it and give due importance for the steam piping design - which is a highly safety related subject, expert's job as expressed, and certainly IT IS NOT A JOB of FOR A BEGINNER.

Thanks.

DHAYANANDHAN.S

__________________
DHAYANANDHAN.S
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dhayanandhan.s (3); MJCronin (6); Naif (1); PWSlack (1); sayed sarhan (1)

Previous in Forum: Torsional Analysis of Motor shaft   Next in Forum: Setting of turbine rotor float

Advertisement