Primary Side of Delta-Star Transformer

03/07/2010 10:52 AM

is 3O/C+1E/F protection necessary at the primary side of delta-star transformer?

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: electrical engg

03/07/2010 2:39 PM

I think o/c & E/F are necessary @ primary side and secondary side .

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#2

Re: electrical engg

03/07/2010 11:41 PM

I think it would depend on what kind of system earthing the delta side or the primary side of the transformer is connected to.

as for me, i would say "yes".. 1 e/f protection would be used to compute the residual currents at the delta side, in which it is unavailable at the high side of the transformer..

Register to Reply
Anonymous Poster
#4
In reply to #2

Re: electrical engg

04/27/2010 6:12 AM

Sub -- Transformer protection Relay, make ABB, Type – RET 650

We are going to install one no 13.5 MVA, ( Pri . volts -- 11000,& Amps -- 708.6 Sec. volts -- 6600 & Amps – 1181.0 ),power transformer, vector group – yNd11,cooling – ONAN, -- at our cement plant at Meghalaya.

The said transformer will be charge with our own captive generation, i.e. 10.50 MW. Diesel Generator set.

Protection Scheme: ---

Code – 27, 59, 81A, 81B, 81C, 81D, 37, 32, 32A. LFR,

Current Transformer -- 2000/1/1, Qty – 4nos, & 1000/1/1, Qty – 03 nos. in your scope.

You are also requested to send your offer i.e. Price, delivery schedule & technical manual etc. subject to all those protections will be covered as per mentioned above protection including NGR.

Your immediate reply will be highly appreciated per return mail.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Primary Side of Delta-Star Transformer

03/09/2010 8:42 AM

If the delta side is connected to an high impedance grounded source or an ungrounded source, then the E/F relay would serve no useful purpose. If the delta side is connected to a low impedance grounded or solidly grounded source, then, yes! the E/F relay would be meaningful. But, even in such a case, the E/F relay so provided would automatically be an REF Relay and would respond to earth faults on the delta side of the windings only. Any star side earth fault will not be reflected on to the delta side lines.

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); electricalexpert65 (1); hkian (1)