Anonymous Poster

Earthing Impedance Formula

03/08/2010 12:02 PM

hello everyone,i would like to ask you a question about earthing empedance calculation following formaulas are for a one ground rod but they are from different sources, R=(ro/2.pi.L).((ln4.L/r)-1) R=(ro/2.pi.L).((ln4.L/r)) now both these formulas calculates the empedance. First one is from BS7430 Second one is from Turkish Standarts. which one is the right one? Which one should we use

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: earthing empedance formula

03/08/2010 12:13 PM

1. Where are you?

2. It's impedance.

Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2

Re: earthing empedance formula

03/08/2010 1:29 PM

Along the line of lynlynch's question...

If under the control of British standards, use BS-7340; if under control of Turkish standards, use that. Another jurisdiction, then ???

I would guess if uncertain which of the two referenced here is applicable, use the larger rods. Is too much earth a bad thing?

__________________
Semper Ubi Sub Ubi
Reply