Generator Response and Tripping

03/09/2010 2:30 AM

hi guys, i would just like to ask for some definitions on the report im working whenever generator trippings occur in our grid...

on the graph several plants like sual 2, ilijan and sta rita suddenly increased their load as the frquency dipped due to tripping of sual 1... what's the term for that response? is it called transient response? why did they return to their original load even if the frequency is not yet normal?

how can i also compute the ideal response of online plants to sudden requency fluctuations???

thank you guys! i need to add some more analysis/recommendations on my report... suggestions are most likely welcomed!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: response of online generators to trippings

03/09/2010 3:41 AM

I probably have more questions than answers, but hopefully some ideas may emerge.... In no particular order:

1. The four already running units responded to the final sudden drop-out of Sual 1, for varying lengths of time.

2. During the Sual 1 "brownout" period (11:03:19 - 11:03:46), San Roque and Sual 2 took on load in good proportion to the wavering of Sual 1.

3. I'm guessing that Sta. Rita 40 and Ilijan B2 were already running at full capacity. After the brief bump upward, they returned within about 10 seconds to their former loadings.

4. San Roque helped out well for about 25 seconds, but then dropped below 90 MW; I'm curious why.

5. Over the whole 2 minutes (11:03:19 - 11:05:16) of this incident, Sual 2's curve conforms best to a scaled inversion of the overall system frequency curve. I would say this plant "saved the day."

6. Did Magat have to be manually started or something? It didn't get into the act for over a minute, and even then ramped up rather slowly in comparison.

7. "Transient response" is a correct term; the 4 running plants seem to have done well in that respect, though 2 of them not for long. (Note 3.) "Ramp-up" would be another good term.

8. Do you know yet why Sual 1 bombed out? I hope it was some little control thing, not an expensive breakdown.

9. What are these various plants? Hydro, steam turbine, nukes in your location?

10. One factor that may be involved in each case is the rotational inertia of the equipment, and how quickly the flow rates of water, steam, or neutron flux can be increased. (Opening valves or gates, feeding oil or coal faster, withdrawing control rods.

11. Interesting question, and best of luck getting to the bottom of this. I hope something in here may be helpful.

12. Welcome to CR4!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jul 2009
Location: Philippines
Posts: 3
#2
In reply to #1

Re: response of online generators to trippings

03/09/2010 4:23 AM

thanks for the reply tornado!

6. Did Magat have to be manually started or something? It didn't get into the act for over a minute, and even then ramped up rather slowly in comparison

yes sir, it was manually dispatched, and it was the scheduled spinning reserve provider for that hour. it did delivered its scheduled 55MW for spinning...

8. Do you know yet why Sual 1 bombed out? I hope it was some little control thing, not an expensive breakdown.

the tripping was due to to boiler feed pump trouble, and not shown in the graph was calaca which also tripped due to under frequency.

9. What are these various plants?

sual- coal fired, magat and san roque - hydro, while ilijan and sta rita are combined cycle plants.

the tripping actuated the automatic load dropping scheme of our grid... i have to prepare a report whenever ALD occurs to the grid or when there is a loss of at least 100MW to the grid. right now we have very low available reserves the reason why we have a very "shaky grid"

Register to Reply
Commentator

Join Date: Nov 2009
Location: PA
Posts: 83
Good Answers: 1
#3

Re: Generator Response and Tripping

03/09/2010 1:49 PM

Hi,

When Saul 1 tripped the other generators have to take the load temporarly. The frequency dip is due to loss of generator. A temporary response is called transient response.

Did you have any load shedding or any other control in the generator going on?

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Generator Response and Tripping

03/09/2010 4:36 PM

Here is what I can see from the graph:

Facts and Assumptions:

The governor of Sual unit 2 is set for isochronous mode (it is swing unit of the system) and all other units governor are set droop mode.

What isochronous and droop mode mean:

Isochronous mode – When operating in isochronous mode the generator will vary its power output as power demand changes to fix the frequency constant. The change of load is primarily absorbed by this unit.

Droop mode –The generator control in droop mode looks at the power system frequency, and adjusts the output of the generator from its nominal set point depending on the extent of the system frequency variation from the target value. The less the system frequency, the more power is delivered by this generator and vise versa.

Analysis:

When the Sual Unit 1 trips, the system frequency drops because the load remains same. As soon as the frequency drops, all running droop units (Sta. Rita 40, Ilijan B2 and San Roque - if I am not color blind) increase their output momentarily. In the mean time, as the system frequency decreases, the isochronous unit (Sual Unit 2) starts responding for maintaining the system frequency constant with the increase of fuel, and hence its output power. The other units then decrease the output power because the frequency increases and the loads keep transfer to the Sual unit 1 from the droop units. By 11:04:19, the loads from Sta. Rita 40 and Ilijan B2 transferred to the Sual Unit 2 and they were back to the original load. The transfer from San Roque was keep going but at 11:04:41, the unit Magat starts and shared almost 80 MW load which has been transferred from San Roque and Sual Unit 2. Finally at 11:06:09, frequency is back to its original and load sharings are stabilized.

The way the systems responds to the failure of Sual Unit 1 is quite normal and the systems works well to respond to the failure and to be stabilized. But again, the analysis is based on the Facts and Assumptions above.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Participant

Join Date: Jul 2009
Location: Philippines
Posts: 3
#5
In reply to #4

Re: Generator Response and Tripping

03/09/2010 9:15 PM

Did you have any load shedding or any other control in the generator going on?

yes sir, as i have mentioned on my recent post, ALD(automatic load dropping) occurred to prevent further decay of frequency.

thank you so much for your replies mr johnson and msamad!

followup question:

lately both sual units are responding strangely. as seen in the graph below, whenever the frequency drops, sual units also drop their generation instead of increasing it? do they have a term for this kind of generator behavior? i think they tweak their governor to disable its transient response capability, can you really disable those functions???

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".