HVAC - 410A Refrigerant In General Repairs

03/14/2010 4:22 PM

Question for discussion; If you are to look at a Hvac system that holds 12#'s of 410A and you determine by all readings taken that the system has lost some of its charge and is not cooling properly and you investigate and find a leaky seal at the brass fitting on the indoor Txv that was not tightened down completely and you make the repair.

Now, lets say it is 2#'s low of refrigerant. Can the method as used in years past with R-22, such as since there was no lines open to air with there being plenty of pressure to keep air out, work with this 410A refrigerant by just topping off the charge with subcool and etc? Or since the 410A is made up of several different refrigerants can you just top it off or should you always reclaim and pull deep vacuum and then weigh in charge?

If the latter of the two is correct, we are screwed with the shade tree type of guys out there doing the first way mentioned and beating us out of a lot of jobs.

Thanks in advance for all comments. I hope to use the knowledge gained, in an up coming service meeting.

Yes, I know there are a lot of things in a real problem to look at, than just the the ones listed above, I am only trying to make a reference so you could see where I am coming from on the question of 410A.

Thanks.

__________________
jhunter1972
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Topic: 410A Refrigerant In General Repairs

03/14/2010 8:52 PM

If the unit has no gauge glass or other means of level detection for the receiver, you may be relying on the liquid line sight glass. If the system charge is too low, there will be bubbles, and you can tell you have added enough liquid when the bubbles stop.

However, a plugged filter/dryer (or other restiction) can create the same symptom, and it may be hard to differentiate. If bubbles persist from these other causes, you might add too much liquid. If it backs up into the condenser, the discharge pressure will rise noticeably. Evacuating and recharging from scratch to the correct weight is precise, but time-consuming.

With the zeotropic blends like 410A, added refrigerant must be in liquid form (inverted canister or 2-valve cylinder).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 132
Good Answers: 7
#2
In reply to #1

Re: Topic: 410A Refrigerant In General Repairs

03/15/2010 12:42 AM

Yes I understand what you are saying but is there any long term damage done to a 410A system that has lost some of its charge and all that is done during the repair is the charge added to the precise amount needed without a completely reclaiming, vacuum and etc.?

I have heard that zeotropic blends leak out at a different rates which can cause the balance of the refrigerant to be off enough that in the long term could cause early failure to the equipment.

I guess I am looking for proof, if there is any, that backs me up when I explain to the customer that taking the short way out doing the repair will cost more in the long run.

__________________
jhunter1972
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Topic: 410A Refrigerant In General Repairs

03/15/2010 2:32 AM

Good point. If the leak was liquid, the remaining composition shouldn't change, and simple replenishment would be okay. But if the leak was vapor, it was probably fractionated, and the remainder would no longer be correctly proportioned.

Evacuation/recharge avoids that problem as well the problem of guessing how much to put in. It costs a bit more, and you should be prepared to explain the reasoning to customer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 132
Good Answers: 7
#4
In reply to #3

Re: Topic: 410A Refrigerant In General Repairs

03/15/2010 8:19 AM

Thank you for your answer, we have been telling our customers that we should evacuation/ recharge to do the job correctly. I now know by your answer for sure that if the leak happens in a vapor state it would probably be fractionated.

Thanks for the info it is much appreaciated.

__________________
jhunter1972
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5
In reply to #2

Re: Topic: 410A Refrigerant In General Repairs

03/15/2010 12:21 PM

I have heard that zeotropic blends leak out at a different rates Since it is a blend of two refrigerants you can explain the temperature glide concept during boiling and condensation. For a non technical customer it will be very difficult to understand this. You have to explain in simple common terms.

Register to Reply Score 1 for Good Answer
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#6

Re: HVAC - 410A Refrigerant In General Repairs

03/16/2010 9:47 AM

If you have a leak from an R-410A system, does the entire charge have to be replaced, or can the system be topped off?

Since R-410A acts very much like a single component refrigerant, any change in composition due to a leak is minimal. The system can be topped off, without removing the entire charge. There is no practical limit to the number of times a unit can be topped-off or the refrigerant recovered from a unit. However, we do recommend that all leaks be repaired before topping a system off. Excessive superheat is an indication of low charge, and the possibility of a leak in the system should be considered.

http://www.epatest.com/R410A/manual/manual.jsp#s

This should answer your first question. Secondly, with certifications & cost of special tools, it should reduce the number of shadetrees.

Register to Reply
Register to Reply 6 comments