HT Motor

03/15/2010 11:48 AM

we have a h.t motor of rating 2000kw,supply voltage 6.6kv. when we started motor tripped on earth fault,then we checked the ir value of motor and found 2MOHM phase to earth and 5 MOHM phase to phase. so i want to know is this value o.k?????????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: H.T motor

03/15/2010 11:49 AM

What is the earth fault device set to?

What were the same set of readings on the cable feeding it downstream of the earth fault device with the motor disconnected?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#2

Re: H.T motor

03/15/2010 11:55 AM

we set earth fault on long inverse(as per IEC STANDARD) Iep-.10 tep-.05 CT RATIO-200/5 MOTOR FLC-203 AMPS.

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#3

Re: H.T motor

03/15/2010 12:01 PM

CABLE I.R VALUE IS OK.

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#4

Re: HT Motor

03/16/2010 7:00 AM

At what voltage did you measure the resistance ? 500V, 1kV, 2.5 kV ??

Cold motor ? warm motor ?

In each case, the 2 of 5 Mega ohm looks not good to me.

We repair electrical motors, and a newly repaired (low voltage 400-690V AC) motor has a resistance of more than 4000 Mega ohm, measured on a cold (+/- 20°C) motor at a test voltage of 1000 VDC.

The minimum I would advise should be at least 100 Meg ohm (testvoltage 1kV)

Keep in mind that when it is foggy outside or the surrounding is humid, the readings will be lower.