Megger Testing

03/16/2010 1:36 PM

how could i make megger test in a plc panel of a water treatment power station designed by schnider electric....

__________________
Thank you........Hema Eissa
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: Megger Testing.....

03/16/2010 2:49 PM

You can Megger anything when not connected to your PLC. Keep that Megger far away from electronics. Semiconductors don't like to be fried or overstressed with your Megger. Even the full electronic Meggers will put your circuits to risk. If you have isolation concerns, use a high (impedance) resistance Ohm meter with limited output voltage on your highest Mohm scale, and overrange display is also ok. (digits flashing)

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#2

Re: Megger Testing

03/17/2010 12:13 AM

Yes, you can megger test; but do not forget to through the panel in to the sea after test completion!

__________________
Subramanyam
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3
In reply to #2

Re: Megger Testing

03/17/2010 12:29 AM

I prefer recycling

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Megger Testing

03/17/2010 3:35 AM

There you have it, do not test anything electronic

but I guess you want to test the other parts of the panel that are not electronic?

If you do , then see if you can isolate or even better remove the PLC from the panel. However I can only wonder why you'd want to megger a panel, if you are trying to test the cables, then disconnect before testing, if its the contactors, they don't really need to be tested.

So think about what you want to achieve and don't just test for the hell of it, you might break something you can't fix.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Megger Testing

03/17/2010 6:07 AM

Megger the cables, sure, if it seems worthwhile or is required by local standards. Make sure they are disconnected from the panel before so doing.

DO NOT MEGGER THE PANEL!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#6

Re: Megger Testing

03/19/2010 2:41 AM

I suggest dont megger the panel :) but insulation test it

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Megger Testing

03/19/2010 3:44 AM

In reply to Guest answer No6,

the word "Megger" is a trade name, but has been used over the years as a way of saying, "let's test the insulation". The correct descriptive name is "insulation tester" for any "MAKE" of tester. It was Avo that called their first tester a "Megger" .

When you "Megger" anything you are testing the insulation, so its one in the same thing. Thought you'd like to know.

BUT..... ALL the previous comments still stand....DO NOT test the PLC/Panel without first isolating or removing the electronics, be safe not sorry!

__________________
The square root of nothing is what you make it!
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (2); dvmdsc (2); kvsubramanyam (1); PWSlack (1)

Previous in Forum: Residential Wiring - NM Cables in Fiberglass Boxes Without Clamps   Next in Forum: Trip Circuit Supervision

Advertisement