Greeting all,
I was reading a topic, it says like this
Hence a cable is almost always a source of lagging reactive power.
Why and what is the reason?
Re: Cables and Lagging Reactive Power
03/17/2010 4:48 PM
I generally avoid power topics - having failed my power class in college, but I presume it's because a cable is basically inductive.
03/17/2010 7:25 PM
check here
Good Answers: 244
03/17/2010 8:57 PM
Cables are considered capacitive load because the insulation between the conductors acts as capacitor. When considered as load, it consumes leading reactive power. When cables are considered as source of power, it supplies lagging reactive power.
How cable is considered as a source of power?
Think about a long cable connecting a generator bus and a load bus and there is no load at the load bus. The load bus voltage will be greater than the generator bus voltage (due to Ferranti effect) and the capacitive nature of the cable causes it. To compensate the additional voltage at the load bus, an inductive load needs to be added. Who supplies power to this inductive load? Generator or the cable? Surely it is cable which causes higher voltage at the load bus. So, cable here works like the inductive source of power.
You also can think the cable as the capacitor bank in PFI. The capacitor bank of PFI also supplies the inductive power which is consumed by the inductive loads such as motors, and hence the power source relives from supplying inductive power which in turn results in less current to supply.
So, 'cable is almost always a source of lagging reactive power' is a valid statement.
- MS
03/17/2010 9:53 PM
Language is a funny thing .
On the first thought the OP statement looked totally wrong. Cable are so obviously capacitive.
So an inductor is a main cause of lagging pf in a circuit. A capacitor is the source for feeding it (the lagging reactive power)
Good Answers: 11
03/18/2010 2:51 AM
Can you give me a reference of any book which support your statement.
03/18/2010 9:29 AM
There is a good article in Wikipedia on power factor.
03/18/2010 10:18 AM
You don't need a book. It is basic of electrical Engineering. read the transmission line chapter where the ferranti Effect is discussed.
Are you not supposed to discuss these in class? After all this is what the professors are paid for?
Good Answers: 11
03/18/2010 10:29 AM
Professor doe not go in depth of topic. So, we have to find and study. I found my question answer as below.
Important results for lossless lines (EHV lines have low resistance, so lossless line approximation is valid).
Voltage profile along the line is flat only if R= Zc is connected at receiving end (SIL). Under this situation, there is no demand of reactive power from either sending or receiving ends. Loads are decided by consumers and not by a system operator. As such, this exact condition is practically never met although it is ideal.
If voltage at both ends is maintained at 1.0 pu (say, by controlling excitation of generators connected at both ends), the voltage tends to sag as we move towards the midpoint if Ps > SIL. The line absorbs reactive power.
If Ps < SIL, voltage swells and the line generates reactive power.
For a line which has one end maintained at 1.0 pu but kept open-circuited at the other end, overvoltage will be evident at the open end.
Cables have very high SIL (why?). The current at SIL usually exceeds the thermal rating of a cable. Therefore a cable is invariably loaded below its SIL. Cables, therefore, generate reactive power and usually voltages can be very high at low loading levels, especially for long lengths. Besides this, cables are much costlier than overhead lines and are more "unforgiving" towards overloads. Therefore, cables of lengths exceeding 30-40km are rarely used for ac transmission.
Good Answers: 244
03/18/2010 7:52 PM
I would say, it is pretty basic concept of electrical power engineering.
You can get it clear with these simple questions and answers:
(1) Does the cable have capacitive nature? -> Yes
(2) Do the capacitors act as source of reactive power? -> Yes
(3) When considered as source, does it supply inductive reactive power or capacitive reactive power to the system? -> Inductive
(4) When considered as load, does it consume inductive reactive power or capacitive reactive power from the system? -> Capacitive
Pay attention to question 3 and 4, both must not have same answer.
Also keep in mind that
Inductive reactive power = - (minus) capacitive reactive power
Supply power = - (minus) consume power
Get it from another set of questions for PFI:
(1) Do inductive loads (motors) consume inductive reactive power? -> Yes
(2) Do capacitors compensate this inductive reactive power? -> Yes
(3) Then how actually capacitors do it? -> Either by supplying the type of reactive power that inductive loads consume (inductive reactive power) or by consuming the opposite type of reactive power that inductive loads consume (capacitive reactive power)
I understand, many times we rely mostly on books and have seen it in math or diagram, but if you think it in more depth, this is what really happening.
These links may also help:
http://www.uni-due.de/ean/downloads/papers/wilch2007a.pdf
http://www.nationalgrid.com/NR/rdonlyres/43892106-1CC7-4BEF-A434-7359F155092B/3543/Reactive_Introduction_oct01.pdf
http://www.alcorn-energy.com/pfc.pdf (try to understand Fig 4)
http://www.tvss.net/pq/pf.htm
http://www.nepsi.com/powerfactor.htm
- MS
03/18/2010 3:18 AM
it is not true .any inductive load is source of lagging reactive power
03/18/2010 10:15 AM
Re read MS's post and the foot note in #4.
It is true.