Fluid Couplings and VVVFs

03/24/2010 10:49 PM

In our plant we currently have a 330 KV electric motor connected to a variable fill fluid coupling to drive a conveyor. We had this setup for the conveyor to run at varying speeds sometimes. We don't require the option of running the conveyor at reduced speed now and the variable fill fluid coupling installed gives us lots of reliability issues. Currently the main reason the fluid coupling is being used is for soft starts for the conveyor to pull away when it is fully loaded.

The question I would like to put to you all is, Can I use an alternative soft starter to replace the fluid coupling? If any one has done this sort of thing, what is the amount of work involved?

I would appreciate any feedback on this

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Can I replace a fluid coupling with VVVF?

03/25/2010 2:07 AM

Your title refers to VVVF, then you mention a soft starter. They are two different things. I also seriously doubt you have a 330,000 volt motor. You probably mean 330kW, about 450HP.

A solid state soft starter varies voltage only. It will start your motor softly, but only within the limits of the motor's thermal capacity. In other words, if your load is such that it takes a long time and a lot of energy to start, a solid state starter may not work, or it may cause a voltage drop. Not as severe as DOL, but sometimes it is still too much. If you have plenty of power, it may still be the better choice, solid state soft starters are typically 1/5 the cost of a VVVF drive.

A VVVF Drive (better known as a VFD) can extend the acceleration time of the motor for as long as possible without adding undue thermal stress to the motor. It's drawback is that even at full speed, there are still losses in the VFD that represent a cost of operation to be considered. Typically this cost would not be as high as that of a fluid coupling however.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Participant

Join Date: Mar 2010
Posts: 4
#2

Re: Can I replace a fluid coupling with VVVF?

03/25/2010 9:34 AM

As guru said, u have to be clear on the voltage rating of the Motor. What is the Capacity (KW) and voltage rating?

What ever it is? however VFD will be very much useful for vary the speed from 0 - 100 %. Do u really require that much variation in the speed?

If u require just for reducing starting current, it is better to go for FCMA (Flux compensated magnetic amplifier) Because the VFD is costlier and u will not use it, once u start the motor. If u keep on vary the speed then u can go for it.

In my previous experience, we used to start 1800 KW (Pump), 11 KV motor with FCMA starter. However the fluid coupling also connected with pump.

Sadhasivam

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3

Re: Fluid Couplings and VVVFs

03/25/2010 11:57 PM

Probably with increasing the speed now, your variable speed controller might deliver a far higher torque at that speed too. Depends on how the system has been conceived. If so, maybe slow starting will not be possible anymore?

__________________
Plenty of room here
Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#5
In reply to #3

Re: Fluid Couplings and VVVFs

03/26/2010 12:36 PM

meant decreasing

__________________
Plenty of room here
Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#4

Re: Fluid Couplings and VVVFs

03/26/2010 4:57 AM

It sounds as though this is a long heavy, conveyor that you have to start under quite a high load.

In this case, the use of a soft start can have some associated considerations:

1. High torque to 'breakaway' will require quite a high voltage and current and then you want to ramp up over a period of time to get your soft start. This presents a high thermal load to the soft start unit which will need sizing to cope with this.

2. Such a prolonged, high current start is also arduous for the motor as well, so you may suffer starting overheat but must provide good motor thermal protection.

3. The above conditions may severely restrict the number of starts/hour for both units.

4. This also presents a very high electrical load during this starting phase giving potential problems on your power supply

Soft starts are not so easy on this type of application, I have run long belt conveyors in quarries on VFD, even these need sizing adequately relative to high prolonged breakaway torque, particularly when its been raining which adds load to the material already on the conveyor. Then, you can also stop and start much more often if needed under certain circumstances (e.g. production is full or halted from upstream)

If you need accurate information, I would recommend talking directly to a specialist e.g. www.fairford.co.uk who have many years manufacturing, development and application experience of soft start units, before you decide which method to use to replace your coupling.

Good luck, hope this helps!

__________________
Something new every day!
Reply Good Answer (Score 2)
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".