03/26/2010 11:48 AM
I set no load voltage of a generator ( in a dredger working in INDIA ) to 415 V at 50 Hz. It work in parallel with other generators for two days. After that when i check no load voltage was 410 V at 50 Hz. How does it changed ?
Re: generator
03/26/2010 1:24 PM
Is it still on noload :))
Re: generator
03/27/2010 12:53 AM
check you AVR
dont say it, write it
Re: generator
03/27/2010 1:12 AM
Once I change the AVR then also happening same. If I want to use generator every time i adjusting noload voltage. There is a filer/suppressor on input line of AVR and it is not earthed. May this can cause the problem ? . The area this generator is working have much noice and vibration.
Re: generator
03/28/2010 11:53 PM
The temperature of the cable is rising,and the resistance is rising,the voltage downs?
Re: generator
03/29/2010 12:31 AM
At initial starting time the temperature is normal, Iam getting low voltage at that time also.