Power Transformer

03/29/2010 4:26 AM

There are two 11Kv/415V , 1000KVA Power Transforemers to cater the factory load of around 800KVA. I want to run one transformer alterantely in every 15 days keeping the other completely switched off from both HT & LT side in order to save power ie no load loss of one trasformer ,considering one 100Kva transformer is capable to run the factory load of 800Kva.

My question is whether the transformer oil and winding insulation will deteriorate for keeping it dead for fifteen days. I shall maintain the silica gel of the breather in good condition.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Power Transformer

03/29/2010 6:58 AM

technically I don't see the reason. And a lot of transformers are kept for this short duration of time unenergised, unless you are in low temperature regions.

Best to contact the OEMs, some of them ask for some heating provisions if the temperature falls below some value, others are not fussy (ours are not ). Our shed is fed from two sides too (2MVA each), and one is kept off for even longer duration.

Reply
Active Contributor

Join Date: Jul 2007
Location: Los Angeles
Posts: 23
#2

Re: Power Transformer

03/29/2010 10:57 PM

Hear is my two cents worth-

I posed a similar question to a transformer manufacture in regards to a solar application. We wanted to switch the transformer off at night to eliminate the NLL.

They said the transformer was not designed to handle repeated inrush currents of re-energization. Better to spend the money on a low loss design.

I think you should alternate transformers less frequently,since you can still run the plant at less the the transformers full load.

Your transformer is Silicon Filled, Indoor? At what temperature will the transformer be at while de-energized. If it is at a mild temperature 75 Degrees F I don't see an issue. Best to always consult the Mfg.

Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#3

Re: Power Transformer

03/30/2010 3:18 AM

The transformer oil and winding insulation will not deteriorate for keeping it dead. What will affect the winding insulation is the process of disconnecting and reconnecting the transformer every 15 days because overvoltages occur. Also the cooling and heating of the tank leads to mechanical stress within its walls.

You also mentioned something about losses. Sometimes it is more economical to have two transformers at 50% load than one at 100%. Just do the math and find out if really disconnecting one transformer will diminish your bill. Consider that winding loss increases with load, and pretty fast.

Another aspect is related to transformer circuit breakers and other switching devices wear. The open/close cycle for circuit breakers adds up to the cost of exploitation.

__________________
The time is ......now
Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#4
In reply to #3

Re: Power Transformer

03/30/2010 7:40 AM

I agree, its has been my experience that electrical equipment run better if they run consistent. Building up heat on a piece of equipment then letting it cool down isn't good for any equipment I now of.

Its better to keep some one my age moving as long as you can because once I stop and fall down, I can't get up. Or is that get it up?

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dda (1); GRAY HAIRED OLD GOAT (1); nikolay (1)

Previous in Forum: Using Power Cables as Control Cables   Next in Forum: How to Find Total Kwh for a Month

Advertisement