100A panel feed #1 vs. #3 debate

04/01/2010 6:35 PM

I am feeding a 100A panel nothing fancy just regular. I typically use 60 degree centigrate wire and terminations for sizes #14 through #1 and 75 degree C from 1/0 and up. Somebody told me since a #3 is good for 100A at 75 degree then that can be used in lieu of the #1 which is 110A's at 65 degree c

thoughts?

__________________
guest
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: 100A panel feed #1 vs. #3 debate

04/01/2010 7:58 PM

T have distributor datasheets for cable. I still use the Graybar or McDonald's (RIP)sheets and notice different types of insulation. If I make my choice, I go for the biggest.

I rather see it myself than hear it say from somebody, because when the inspector comes somebody in trouble will be me. This question is like frying eggs in teflon coated pan or not.

__________________
Plenty of room here
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: 100A panel feed #1 vs. #3 debate

04/01/2010 8:11 PM

I'll assume that you are in North America and you are referring to AWG ratings in your descriptions.

But where the heck are you getting your information? There is no #3 AWG building wire available commercially, so if you are reading off of a chart from a wire manufacturer it is meaningless. The only thing that counts is the NEC table that pertains to the specific installation requirements you must follow for your situation. Above ground, free air, underground, in raceway, how many conductors with it, voltage drop over distance etc. etc. etc. all contribute to which ampacity table you must use. Get yourself a copy of the NEC and look through the myriad of charts in Article 310.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: 100A panel feed #1 vs. #3 debate

04/06/2010 3:13 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856