dear all,
On 5th april 2010 , Electrical Preventive maintenance was done on ash handling compressor -1.
The following works was done
1. Cleaning the compressor motor,
2. cleaning of the blower motor,
3. Checking the tightness of the terminals
4. Checking the main contactor,
5. Insulation resistance >550 mega ohm equal in all phase to earth.
6. Winding resistance = 0.13 ohm equal in all phase.
The trial run was taken , the motor was started and tripped suddenly. The indication in the local panel was "FC " and the motor overl. The electrical engineer checked the motor insulation resistance >550 Megaohm and winding resistance = 0.2 ohm.Opened the contactor and checked, it is normal.
1 litre of oil was filled .
When they started the motor , our auxiliary transformer got tripped due to earth fault..The plant Block out was ocurred.
Specification:
The compressors make INGERSOLL RAND
Capacity - 125 HP
Voltage - 440 V
Current - 146.6 A
RPM - 1785
P.F - 0.87
Frequency - 60 HZ
Connection - star delta
overload setting for the motor - 145 A
Incomer breaker details for the compressor -1
Make : siemens
Type: 3WT8
In - 800 A
SETTINGS
Inverse time delay overload tripping Ir - 0.8 x In
Short time short circuit tripping Isd - 3 x Ir
instataneous short circuit I1 > 15 In
Earth fault tripping Ig - 0.3 x In