Upgrade UPS Power Distribution Board

04/11/2010 10:53 AM

Dear Guys,

In our plant, we want to upgrade existing UPS PDB (ACP-01) to new one with different main breaker rating to accomadate new load.

Present condition (ACP-01):

- Got feeder from other UPS PDB (ACDP) with breaker 70AMP, 120VAC.

- ACP-01 Main breaker 60AMP.

- We don't have existing load calculation or any documentation (lost).

- We measure existing load is 14.5Amp.

Upgrade:

- We want to change with new PDB (ACP-01) with the same feeder from (ACDP).

- New load will be 17kVA.

Is it possible we accomodate that 17kVA load?

Thanks.

__________________
- I will ask for something I dont understand to you -
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Upgrade UPS Power Distribution Board

04/11/2010 12:26 PM

The new load of the upgraded ACP-01 is 17 kVA. The current of the new load is 17,000/120 = 142 A. The ACDP breaker capacity needed is 142 x 1.25 = 177.4 A (~180 A). If you know the load diversity (or redundant load), the calculated rating may less than this.

The existing UPS PDB (ACDP) feeder breaker is 70 A only, so the breaker is under capacity.

You also need to make sure:

(1) The UPS capacity, ACDP and other UPS components are of enough rating to accommodate this new load including the other existing loads.

(2) The cable from ACDP to ACP-01 can carry the new load current. The cable ampacity shall be at least 180 A with voltage drop is witin 3%.

(3) The proper coordination of the breakers and fuses.

There are many other things to consider as well. So, I would suggest doing a thorough study of the UPS system before adding the new loads.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Upgrade UPS Power Distribution Board

04/11/2010 7:15 PM

Camelito Quote "Got feeder from other UPS PDB (ACDP) with breaker 70AMP, 120VAC"

Are you sure the voltage is 120 volts. It is very unusual for a load that large to be using 120 volts. Sure it isn't 240 or 480 volts? Maybe 3 phase.

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Upgrade UPS Power Distribution Board

04/11/2010 8:25 PM

The way the Camelito described it is UPS PDB (ACDP) is main distribution panel and ACP-01 is subdistribution panel. The 70AMP breaker in ACDP is feeding the panel ACP-01. In this case the 70AMP, 120VAC is logical. Camelito can confirm it.