I am looking for info/formulas to calculate sizing of generator.Torque reqirements of (x)KW generator cutting full load flux at (x)KW rated output.Also to calculate torque availabilty of mover (x)wk2 rated /to running at a reduced shaft load.
Also, for efficiency in bhrescobar's formula you could insert 90% and not be too far off -- if you are only looking into feasibility for a small generator. If a few percent one way or another equates to a large amount of money, then you'd need details on the particular generator, prime mover. etc.
__________________
There is more to life than just eating mice.
The power calculation of a generator set is done with an expected life and an expected power percentage average. For short periods, it will and can give more power. A generator set for continuous power is way bigger than the same power for emergency use.
A motor power (can also be done in kW) is the absolute max power that it can give continuously in a certain environmental temperature, pressure and humidity situation. This is a figure that also gives a good idea of what you can do with the motor but it can't be taken as the startup power, it is this startup effect (getting your machinery from 0 RPM to the work speed) that is determining to power of your motor. Each motor has a 0 RPM torque, which needs to be greater than the torque needed to get your machine working. It is seldom that your motor is running at the power as denoted on the type plate.
It is not because you have a 100 kW motor that it will speed up till your machine consumes 100kW. (it is like the problem when you replace a 60 W bulb with a 20W , you will only get less light and your 20 W bulb will not explode)
__________________