I'm trying to power the space heaters in a 25MVA auxiliary transformer, but it wont come up.The power supply to the control panel has a mechanical interlock and the input to the panel comprises of supply1 and supply 2(415Veach).But am powering just supply 1 and the under voltage relay in the interlock circuit keeps triping and this action prevents the magnetic contactor from closing and as such power does not flow to molded case circuit AC control power that delivers power to the breaker for the heater.whenever i switch the breaker on that controls the mechanical interlock section the undervoltage relay closes and then opens and thus prevents the magnetic contactor from closing.
Pls if anyone has ever powered up the heater of such a transformer before i'll be pleased if he or she can help me out.Thank you
Transformer Specs
Hyundai Heavy Industries
25MVA Auxiliary Transformer(HHI)
15kv/6.9kv DYN1 ,OLTC
Re: Powering of space heater in a transformer LCP(local control panel)
04/12/2010 2:55 PM
Am I missing something here or is your undervoltage relay sensing that supply 2 is unpowered and so tripping out on undervoltage alarm? This explanation makes the most sense.
A simple way to fix this could be to parallel connect the two supplies (1 and 2) together, BUT YOU must check the manuals and datasheets and manufacturer's literature to ensure this is possible (and safe) BEFORE you attempt this. There must be a reason why there is a second supply to the panel (redundant power feed perhaps).
Check the manuals and datasheets as there should be adequate explanation as to the operation of the interlock, undervoltage release and dual supplies. Let us know what you find.
04/12/2010 4:58 PM
Thanks for your answer.
The two supplies have their own seperate undervoltage relays and seperate breakers to take in power to the interlock circuit,so i felt powering one supply will not be a big deal.am wondering if my connection is wrong.I connected a three phase(no nuetral) directly into the circuit as shown in the diagram but the secondary side blends with the 3 phase and has the fourth terminal strongly earthed.My line to line is ok and my line to nuetral is also good.
NB
what is a CAM selector switch?i suspect this is the problem
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member
Re: Powering of Space Heater in a Transformer LCP (Local Control Panel)
04/13/2010 2:44 AM
u ve to use 2 uvr for the 2 supplies such tht when one uvr is energised the other shouldnt get energised........this s done in the control circuit of the uvr and the contactor...........
shamith gambhir, electrical engineer
04/13/2010 8:47 AM
Forgive my ignorance and a quick Google search didn't get me any answers, but I was curious why a large transformer such as this would need a space heater? Is it to keep it dry when not being used? I'm assuming this is a dry transformer and not an oil-cooled unit.
04/13/2010 5:21 PM
Dear friend,
Kindly check your installation, operation and maintenance manual of your equipment. analyze also the schematic and wiring diagram of your local control panel how these two power provisions are being opted to supply your transformer's heater when needed. I am sure there is a protection/interlocking contacts or safety device integrated in your control circuit preventing the closing of your magnetic contactor to switch on the power supply for transformer's heater.
I do hope this simple idea of mind will help you.