1 Core Cable vs. 4 Core Cable

04/13/2010 12:46 PM

Hello to all members here. We are planning to lay a distribution cable from Utility sub station to our Distribution panel. The distance between the sub station and Distribution panel is about 325 meters. Based on our design load we need the cable with size of 630 sq. mm. our supply voltage is 380 volts, 3 phase, 60 hertz. The cable will be directly lay to the ground of about 1.2 meters deep. Our ambient temperature (max) is about 55 *c during summer. We are in Saudi Arabia. initially we plan to lay a 4 core cable. But because of the cost our supplier recommend to use 1 core cable only with the same size. Now my question is, it is okay to use 4 x 1 core cable instead of 4 cores cables? Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 1 Core Cable vs. 4 Core Cable

04/13/2010 3:15 PM

The short answer is yes you can use single core cables instead, but check your electrical standards and local electrical regulations for more details and correct laying, spacing and burying procedures as there are some requirements that differ from using a single 4-core cable.

Additionally there have been some previous threads on CR4 that may be of help, especially when trying to pass three-phase single core cables thru steel (these can be found using the search engine on the right).

__________________
jack of all trades
Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 42
#3
In reply to #1

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 12:26 AM

thanks a lot for your help.

Reply
Anonymous Poster
#2

Re: 1 Core Cable vs. 4 Core Cable

04/13/2010 11:46 PM

Yes you can use 4 individual single core cable instead of 4 core cable.

Reply
Associate

Join Date: Nov 2009
Posts: 42
#4
In reply to #2

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 12:27 AM

thanks

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 2:21 AM

Selecting and laying power cable for calculated load can be easily refer back to the cable manufacture data sheet. Selecting for the correct and the ways to select the mothod to lays these cable is alwaya depended upon the experiences of the engineering department or the electrical consultant advice.

From your question above, I don't have your total load of your requirements but base on your cables selected of 630 mm2 and the distance, I do believed that your total load will be some where about 700 Ampere.

There is two ways that you can do to select your cables.

1) You can use two length per phase of single core cable of 150 mm2 where each cable current capacity of 345 Amps. = 690 Amp

Or

2) 2 length of 4 core 240 mm2 per phase with each cable current carrying capacity of 360 Amp. = 720 Amp

At the final stage you need to balance up the costing of your projects to see which method is suitable

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Associate

Join Date: Nov 2009
Posts: 42
#7
In reply to #5

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 2:27 PM

thanks for suggestion. actually the 630 sq mm cable is for assume design load only. our actual design load but not final yet maybe around 2200 amps @ 380 volt distribution. at 320 meters distance from substation if i use 4 cores cable is very expensive. that is why i am asking for help if posible to use a 1 core cable only which is cheaper compared to 4 cores. considering it will be directly burried to sandy soil here n saudi arabia i worried about the effect to insulation. my other option is to apply to power company to supply us a 13.8 kv feeder near our distribution panel and we will ill use a step down transformer. our request is still under pendingy. our 2nd option is to use the existing substation but the distance is 320 meters

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#8
In reply to #7

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 8:11 PM

Actually, we can't give you much details on the cables sizes that you will used. Distance is not the problem as there is some calculation, K-factors to be consider and the faults level need to be calculated for the total load connected for the single core cables. In my recently project my cable distance is even longer than your distance that is about 800 meters from the main sub station.

It depends upon your required load. IF you need a very high ampere then, it is better to install a transformer at the site and apply for 13.8KV from your local electricity authorities. It will be much better.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 42
#9
In reply to #8

Re: 1 Core Cable vs. 4 Core Cable

04/15/2010 2:53 PM

thanks a lot

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: 1 Core Cable vs. 4 Core Cable

04/14/2010 7:34 AM

British Standard 7671 encompasses algorithms that can be used to determine this.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#10

Re: 1 Core Cable vs. 4 Core Cable

04/24/2010 1:43 AM

Here in Saudi Arabia though SCECO in Central, Eastern and Western Region have there different standards of installation. As usual practice at MV/LV substations relevant to your distance between SCECO substation to MDB we recommend to use a directly burried 4cores cable type XLPE/CU/PVC/SWA or XLPE/CU/PVC/STA. Neverthelss you can use single core cable provided it must be in PVC conduit sleeve or ducting. Minimum deep of directly burried cable allowed by SCECO is 0.80m for LV and 1.20m for MV. Any LV cable/s in trench entering into the building premises or around the loop outside of the building the minimum distance between the energized cable and telecom cable shall be 0.50m apart.

__________________
If there is a will... there is a way... No pain / No gain.
Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#11
In reply to #10

Re: 1 Core Cable vs. 4 Core Cable

04/24/2010 2:21 AM

One option is overhead installation normally 22KV/380V rural tpye. Here in Saudi Arabia it is pretty hard to get the approval from Saudi Consolidated Electricity Company(SCECO) since plenty of justification needs to be done and its a marathon issue. Minimum charge for MV transformer tap at RMU cost us Saudi riyal 125,000. So instead of paying this connection fee , the option is go back to LV underground installation if the distance is minimal.

__________________
If there is a will... there is a way... No pain / No gain.
Reply
Associate

Join Date: Nov 2009
Posts: 42
#12
In reply to #10

Re: 1 Core Cable vs. 4 Core Cable

04/24/2010 8:51 AM

thanks a lot. your suggestion will be very helpful for my decision later o.

Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Dalton (5); hentoyk (2); jack of all trades (1); PWSlack (1); Simon Wan (2)

Previous in Forum: VCB Selection Procedure   Next in Forum: Testing Relay at 70hz
You might be interested in: Cable Laying Services, Cable Assemblies

Advertisement