How To Calculate Cable Burden

04/18/2010 6:08 AM

what is mean by Cable burden ? how to calculate burden value of cable?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Mr

04/18/2010 8:49 AM

You don't really give enough information to explain which possible version of cable burden you have. You might be talking about the equations that make a catenary curve. You may need to know the tensile strength of a cable. You could even be referring to collisions in computer science. Lastly you might even be wondering about the harness strength for your donkey.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Cable burden

04/18/2010 10:55 AM

The cable burden is the load (in VA) imposed to CT secondary due to the cable resistance. When considered the CT load, the cable burden is also added to the other loads used in CT secondary.

The CT secondary load = Sum of the VA's of all the loads (ammeter, wattmeter, transducer etc.) connected in series to the CT secondary circuit + the CT secondary circuit cable burden.

Cable burden = I2 x R x L

Where

I = CT secondary current,

R = cable resistance per length,

L = total length of the secondary circuit cable.

If the proper size and short length of wire is used, cable burden can be ignored.

See also http://cr4.globalspec.com/comment/448082

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Register to Reply 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

Previous in Forum: Single Conductor Interturn Fault   Next in Forum: Star Delta Diagram
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement