Single Conductor Interturn Fault

04/18/2010 4:36 AM

A generator conductor consists of several no of small conductors as in case of water cooled conductors of large generators. Each Small conductor is insulated from other conductors. If this interturn insulation gets damaged, How to detect it?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#1

Re: single conductor interturn fault

04/18/2010 5:53 AM

For larger units either a transverse differential relay or a neutral displacement relay can be used depending upon the system arrangement.

__________________
Better not count the cent if the risk is many many dollars.
Reply